if you have 1 appliance ie glowworm ultimate 50ff supplied from meter done in 15mm pipe supplying only 1 appliance. no other appliances on meter,
checked operating pressure at gas valve, 17.45 mb ,
dont want to check pipe before valve as all pipework is buried, and would make sh**te of the job.
have close to 9 meters of 15 mm supplying boiler.
( 1.5cbm/hr ) as per manual
could really have been brought up to 22 mm pipe but wasnt. (typically)
when gas rated boiler its using 1.62cbm/hr
which appears to be within range as per plate
16.64 kw/ 10.4mb 1.54cbm/hr
18.32 kw/ 12.6mb 1.70cbm/hr
now the question is
boiler allowance 1 mb drop from meter to appliance.
actual drop 21 mb down to 17.45. on gas valve maybe a further drop on valve
but appliance only needs 12.6 mb
what i have is
1.62cbm/hr 17.43kw @ burner pressure 11.45mb
so summarise all the above would i be correct in saying .
as long as you are getting the required pressure above burner pressure requirement all should be well.
all coments appreciated.
checked operating pressure at gas valve, 17.45 mb ,
dont want to check pipe before valve as all pipework is buried, and would make sh**te of the job.
have close to 9 meters of 15 mm supplying boiler.
( 1.5cbm/hr ) as per manual
could really have been brought up to 22 mm pipe but wasnt. (typically)
when gas rated boiler its using 1.62cbm/hr
which appears to be within range as per plate
16.64 kw/ 10.4mb 1.54cbm/hr
18.32 kw/ 12.6mb 1.70cbm/hr
now the question is
boiler allowance 1 mb drop from meter to appliance.
actual drop 21 mb down to 17.45. on gas valve maybe a further drop on valve
but appliance only needs 12.6 mb
what i have is
1.62cbm/hr 17.43kw @ burner pressure 11.45mb
so summarise all the above would i be correct in saying .
as long as you are getting the required pressure above burner pressure requirement all should be well.
all coments appreciated.