Hi lads.
Just realised I'm about to remove a Potterton combi which has 15mm gas feed.
A MAIN combi going for installation and the pipe size is 22mm
Pipework is totally concealed atm and there's about a 1500mm of 15mm accessible pipe run to the old Potterton
Is there such a fitting or a solution.
I can quite easy understand if it was the other way round
Do have to upgrade the pipework from the meter all the way to the boiler?
There is sufficient gas supply from the meter which is about 2.5meters away.
It has 26 mbars standing pressure and a 20.5 mbar working from the meter.
There was a cooker which is capped off and cooking on electric.
No other gas appliances in the place.
Cheers
Spanner