Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss increase pipe size in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

spanner

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,237
Hi lads.
Just realised I'm about to remove a Potterton combi which has 15mm gas feed.
A MAIN combi going for installation and the pipe size is 22mm
Pipework is totally concealed atm and there's about a 1500mm of 15mm accessible pipe run to the old Potterton
Is there such a fitting or a solution.
I can quite easy understand if it was the other way round
Do have to upgrade the pipework from the meter all the way to the boiler?
There is sufficient gas supply from the meter which is about 2.5meters away.
It has 26 mbars standing pressure and a 20.5 mbar working from the meter.
There was a cooker which is capped off and cooking on electric.
No other gas appliances in the place.

Cheers
Spanner
 
You were never going to get sufficient gas down 15mm for a combi.
 
Seen loads of combi with 15mm pipe and perfect working pressure from meter reading to combi before!
Just this is awkward it has 22mm from the meter then under flooring and up in 22mm. Which has a run of 1200mm from the wall
Sounds like it'll have to be
 
You will only know the drop for meter to boiler once it's fitted unless you can test the existing.

What size combi are you fitting?
If it's only 2.5 meters from meter to boiler you may be lucky
 
just change the 1.5m to 22mm then test pressure.
i think it will be ok.
 
Status
Not open for further replies.

Similar plumbing topics

Ok I think I see what your saying mate, So...
Replies
9
Views
727
More than fine then in 11/5 tube should be...
Replies
3
Views
629
Thank you for the replies. I had another...
Replies
4
Views
836
I get 1.65mB drop plus fittings for 30m in...
Replies
18
Views
4K
Unfortunately just because it works now...
Replies
6
Views
5K
Back
Top