Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss install new central heating system in the Central Heating Forum area at Plumbers Forums

Messages
14
Hi All,
I am very new to all this so forgive me if I am lacking alot of knowledge. Aiming to install a new central heating from scratch.
Property details
  • split over 3 floors
  • 4 bedrooms
  • 2 bathrooms
  • open plan kitchen/lounge
Current Installation assumptions
  • install 8 rads in total running off a combi boiler
  • 15mm plastic
Question
  • as it is split over 3 floors does it make sense to have zone valves for each floor?
  • do I need an additional pump to cover the 3 floors? additional expansion vessel?
  • Planning on using 15mm plastic, should I be considering 22mm instead?

Attached is a photo showing the layout I plan to run the central heating pipes. Any advice would be appreciated if it looks wrong.
IMG_4224.JPG

Many thanks
 
As it’s from scratch/ new you will need to bring it upto current regs eg new rad sized for 55dc flow and 28mm pipework
 
You need heat loss calculations first of all. Done by a tried and tested, accurate method.
You will need to size heat emitters correctly to give the right output at 55 degree flow (as Shaun said). See part L of building regs.
You will need to calculate the pipe size going off route and volume of water to be carried, pressure losses etc.
You will be better off with 3 zones in my opinion. Each with its own controls.
You will usually size the pump off the above findings and may need to adjust things to suit. With a combi boiler you need to know what is left in
15mm plastic is only capable of around 20,000 Btu but that depends on things like route, fittings, valves etc. It can be less.

Hope this helps.
 
Its not the sort of job for a novice you would be far better off employing a professional, your plans contain errors already pipe sizing is very important heating over 3 floors will require 28 mm flow and return for a good few meters , a combi boiler is really only meant for smaller properties hot water supply is limited to one or two taps at best. . Kop
 
thanks all for the feedback. looks like its not as straightforward as I hoped. lots more research to do then and I'll see if I can get an experienced plumber to work along side
 

Similar plumbing topics

If you are paranoid, refill, circulate and...
Replies
2
Views
293
Replies
17
Views
2K
B
Context for issue: I'd like to start by...
Replies
0
Views
559
Butchy10
B
R
I need advice on flushing out my central...
Replies
0
Views
838
Robin Overall
R
Its a Combi. Its a Worcester Bosch Greenstar...
Replies
8
Views
1K
Back
Top