installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the ratio ok | Gas Engineers Forum | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the ratio ok in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

if it says in th mi's it should be 0.0004 then your reading is too high. Are your gas pressures and flueing ok?
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

gas pressures ok, mi say 0.004 not 0.0004? flue is ok...wat u think?
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

Are you sure you're reading it correctly? You may have got the decimal point in the wrong place.
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

Where are you getting the 0.004 from?

The reading should be around 0.0015 on max and about twice that on min. Check the book. I can't remember.
Check your pressures and make sure it is set to high fire and also check it at min.

Btw this is a band B and you shouldn't really be fitting it.
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

As per tamz previous post. Firstly, is the Compact HE not a 'Band B' bellow 90% efficiency? How can you be fitting that?

Secondly, looking at your ratio figures.
Where are you getting 0.004 from exactly? The MI's I looked at state a max ratio of 0.001, so your 0.0011 is more or less spot on.
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

no its a grade A boiler. i did the settings on high and low flame, then did the combuston test after.it says in the m,i that if the boiler should b running at a ratio of 0.004/1 or below is ok, anything over 0.008 is a,r? the comustion test i got 0.0011. is this ok, please help?
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

As per tamz previous post. Firstly, is the Compact HE not a 'Band B' bellow 90% efficiency? How can you be fitting that?

Secondly, looking at your ratio figures.
Where are you getting 0.004 from exactly? The MI's I looked at state a max ratio of 0.001, so your 0.0011 is more or less spot on.


its a grade A new boiler.....0.004 says in m,i its running gud, 0.008 or above its a,r.....i got 0.0011 do u think my readings r ok?
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

no:frown2::thumbs_down::frown2:
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

The MI's usually state the max the ratio can be. If it states 0.0040, much like ideal icos and isars do I believe, then a reading of 0.0011 when running on max is absoloutely fine. I am not familiar with this boiler, does it state a co2 percentage or a co ppm count? If it does have either of those, aslong as they are all within the guidelines given it is fine.
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

0.0011 is fine but check the % to see if it tallys up to mi,s it should be around 8.7%
 
Last edited by a moderator:
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

0.0011 is a good reading usually action level is 0.004 but check mi instructions because Worcester are 0.002 so always go with mi - readings getting worse would be 0.0008 then 0.0009 then 0.0010 then 0.0011 etc but check your %
 
Last edited:
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

its a grade A new boiler.....0.004 says in m,i its running gud, 0.008 or above its a,r.....i got 0.0011 do u think my readings r ok?

So it's a compact A you have fitted and not a compact HE! Your readings are fine. 0.0011 is nearly 4 times lower than 0.004.

Not a boiler i am familiar with but i just looked up the manual

This is the readings you should be getting
2.11 Emissions Compact 29
CO2 @ maximum output (%) 9.0
CO2 @ minimum output (%) 9.5
CO @ maximum output (ppm) 160
CO @ minimum output (ppm) 35
NOx rating class 5 class 5

It doesn't state what the expected ratio should be but you can easily work it out.
160/90000 = 0.0018 (rounded) at max and 35/95000 = 0.0004 on min
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

A maths tutorial should help to determine which no. is smaller or bigger
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

A maths tutorial should help to determine which no. is smaller or bigger

the ability to see a thread is years out of date can be useful as well
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

Moved off open forum.
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

Why is this stil going??????
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

closed thread
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

Delete
 
Last edited by a moderator:
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

How did an unregistered guest get in to the private gas safe forum?

didnt crop moved after to pgsf
 
Re: installed a new vokera 29he compact natural gas, the ratio is 0.0011? is the rati

Good information is never out of date !!! [emoji12]
 
Status
Not open for further replies.

Similar plumbing topics

Have you cleaned the heat ex?
Replies
10
Views
2K
Thanks for your response mate. Im not...
Replies
2
Views
769
Set whatever boiler you're installing to the...
Replies
2
Views
920
When they converted to northsea gas in the...
Replies
3
Views
603
Back
Top