Just moved into a new house and this is driving me crazy. Some mornings I have hot water and other mornings its luke warm.

Not sure if the central heating needs to be on at the same time to warm up the water - tried it on and doesnt seem to make too much difference.

I'm a bit confused over all these things.

Upstairs we have 2 showers and in the closet there is:
Vented Cylinder
1 x Salamander CT50 (Searching online this is a shower pump)
1 Grundfos Alpha 2L 15-60 (Pump)
1 x Drayton LP522 (Hot water and central heating programmer)
1 x Honeywell (programmer? Seems to be off - no lights on)

Downstairs is a Ideal HE18 boiler.

Not sure if this is enough info to work out what's going on but what is the Grundfos pump for? What does the Honeywell box do?

I've read on few threads saying the central heating needs to be on at the same time as the heater for the water - is this true?

Was going to post a pic but there seems to be a limit for new users.

Drayton on left wall, honeywell - white box on floor left. Has 3 buttons and a light indicator.Then there is another white box on the right - no label. Grundfos on top, Salamander bottom.
 
Sounds like you may have a wiring or a control fault. I would be tempted to get a heating engineer in as it's hard to comment without eyes on the set up
 
Have you tried setting both heating and hot water to constant on the programmer? That will keep your hot water hot at all times as the cylinder thermostat will control that. Then control your heating via the room stat. If that works then you can go through the manufacturers instruction book on setting your hot water and heating or simply leave it as it is. If that doesn't work then you may have a wiring fault or a faulty zone valve
 

Similar plumbing topics

  • Question
That’s good, we’ll persevered! Let us know...
Replies
11
Views
1K
Looks that way, a multimeter would tell alot...
Replies
8
Views
977
  • Question
Prob using the blue core from the cylinder...
Replies
9
Views
2K
What he said. Looks like 15mm copper conns...
Replies
7
Views
2K
Thanks mate. Been very lucky, a neighbour...
Replies
3
Views
2K
Back
Top