Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss IQE / Sime wiring in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

AWheating

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
9,864
goto wire a iQE 30bag of pants combi. have yet to go and look at it but looking at the manual it has volt free only connection for external controls. The wireless stat that has been brought can be wired to this but does anybody know a volt free frost stat and pipe stat set up i can connect to this? or am i going to have to use a relay of some sort?

any help will be appreciated, especially if anybody has a link to a drawing ;)

this is the instruction manual, little to no help on the wiring tbh.

http://www.iqe.co.uk/sites/default/files/iQE Simplicity -Installation Manual_0.pdf
 
Page 16.

Room stat; connector CN6 term 7 + 8

Frost Stat; connector CN14 term 14 + 16
 
I was unsure you could use both ? As the instructions say "or" so I assumed one or tuther. Probably my understanding of the English language causing me confusion , I'm easily confused on Sunday mornings :) I'll try it and see what happens.
 
Last edited:
If not just put two wires in to each of the room stat / programmer holes. Take one from each connector to the room prog/stat and one pair to stat.

To test simply turn stat off and out frost stat on. 30 . This won't work tho if you have internal programmer. Think it's 1 and 3 on stat.
 
iQE 30 ...has volt free only connection for external controls.
Not according to the manual you link. See the Note on pages 15 & 16.

does anybody know a volt free frost stat and pipe stat set up
The Honeywell T4360 frost stat and L641B pipe stat can be used volt free; they are just temperature controlled switches! The frost stat does not have an anticipator, so there is no requirement for a mains neutral connection.
 
Last edited:
Status
Not open for further replies.

Similar plumbing topics

Yes some are linked internally eg Drayton...
Replies
9
Views
1K
I have a home with an oil boiler in a garage...
Replies
0
Views
634
I thought it would be good manners to give an...
Replies
4
Views
3K
Piece of thin metal bent like half moon so it...
Replies
5
Views
919
P
Mr Speaker: I'm tempted to draught a sarcastic...
Replies
22
Views
4K
Back
Top