Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Is this an Oversized boiler? in the Boilers area at Plumbers Forums

Messages
13
hi all,
First post, mostly been lurking about.

I have an issue with my Baxi Solo pfl 50 short cycling. It runs fine for about 45 mins when system starts from cold then starts cycling on its stat about 5 mins on then 5 mins off. I’ve checked flow and return temps from boiler and shows it’s definately cycling on the stat. It does this until the hallway stat is satisfied. I’ve checked radiator balancing and tried pump speeds but doesn’t seem to help. Just added up the radiators outputs at 26000 btus, with this in mind would you expect to see that kind of cycling with a 50000 btu boiler? Cheers
 
Baxi solos are old has it just started doing this ?
 
hi all,
First post, mostly been lurking about.

I have an issue with my Baxi Solo pfl 50 short cycling. It runs fine for about 45 mins when system starts from cold then starts cycling on its stat about 5 mins on then 5 mins off. I’ve checked flow and return temps from boiler and shows it’s definately cycling on the stat. It does this until the hallway stat is satisfied. I’ve checked radiator balancing and tried pump speeds but doesn’t seem to help. Just added up the radiators outputs at 26000 btus, with this in mind would you expect to see that kind of cycling with a 50000 btu boiler? Cheers


Boiler may be over sized for the system, it has probably always done that.
Have you calculated the Heat requirements for the property?
What size of Domestic Hot water Cylinder do you have?
 
I did have a look on the net about heat requirements but couldn’t find anything that useful, it’s a 15 yr old townhouse with three beds and 9 rads in total. The cylinder is an rm cylinder 120l. The boiler fan (I think) is a bit noisey and I think that’s the reason I have noticed the short cycling. Basically I’m thinking either spend x amount on getting the boiler fan replaced and boiler serviced or replacing completely for something modulating that’s going to save probably quite a bit of money esp if this short cycling is due to it being oversized
 
I did have a look on the net about heat requirements but couldn’t find anything that useful, it’s a 15 yr old townhouse with three beds and 9 rads in total. The cylinder is an rm cylinder 120l. The boiler fan (I think) is a bit noisey and I think that’s the reason I have noticed the short cycling. Basically I’m thinking either spend x amount on getting the boiler fan replaced and boiler serviced or replacing completely for something modulating that’s going to save probably quite a bit of money esp if this short cycling is due to it being oversized
As demand is 26000BTUand boiler output is 50000, equal times on and off is about what you'd expect. Is it a problem?
I'm not sure on/off operation in itself is much less efficient than modulating, but a new boiler would be more efficient for a number of reasons. However, it would take a good many years to recover the cost.
 

Similar plumbing topics

I'm sorry it's been difficult reading. Is this...
2
Replies
37
Views
4K
So you don’t have any of the blending valves /...
Replies
3
Views
2K
Seemed so, for that first half hour. House had...
Replies
12
Views
5K
No I do not. Second to that I don’t even have...
Replies
3
Views
1K
Below is a sizing chart based on a heat loss...
Replies
1
Views
791
Back
Top