This is a flue I have come across today whilst doing my first landlord certificate. It is on a Worcester 24i RSF-L.
There was duct tape on the join in the flue;and the flue elbow connected to the boiler with a jubilee clip and there were no screws.
I removed the tape and tested the flue gas which was fine (incoming was 20.9 O2 and exhaust was 11PPM CO and ratio 0.0002). I put a self drilling screw in the join where the flue and extension met and put the foil tape around (as it was taped before). I tested the room CO which was 0 and fitted a CO alarm to the ceiling.
I isolated the boiler and said I would be back in the morning.
Is this flue correct?
There was duct tape on the join in the flue;and the flue elbow connected to the boiler with a jubilee clip and there were no screws.
I removed the tape and tested the flue gas which was fine (incoming was 20.9 O2 and exhaust was 11PPM CO and ratio 0.0002). I put a self drilling screw in the join where the flue and extension met and put the foil tape around (as it was taped before). I tested the room CO which was 0 and fitted a CO alarm to the ceiling.
I isolated the boiler and said I would be back in the morning.
Is this flue correct?