Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Is this gas restrictor elbow fitted correctly? in the Gas Engineers Forum area at Plumbers Forums

Messages
3
Hello
The gas restrictor elbow in the picture was fitted by a gas safe engineer. The gas fire is on the left and the supply is on the right. Has this been fitted correctly?
Thanks
 

Attachments

  • gas restrictor elbow.jpg
    gas restrictor elbow.jpg
    244.9 KB · Views: 75
No
 
Many thanks for your replies. The elbow is new and was fitted a few weeks ago to the supply pipe which is old. The previous original elbow was fitted differently (the inner and outer screws pointed towards the gas supply pipe). However, for the new replacement elbow, the inner and outer screws point towards the gas fire. Should we ask the gas safe engineer to refit it and what reason should we give? Or is it OK to leave it as it is?
 
It is installed the wrong way round from a design & use point of view and will not shut the gas off as intended (in other words, it is fairly pointless).
That alone is enough reason to have it correctly installed. As it is it will probably isolate the fire but not without allowing a large amount of gas to escape whilst closing it down and replacing the top outer cap & washer in your case, to stop gas escaping. You would really need to turn the gas off (at the meter most likely) to be able to isolate the fire safely.

I suspect they put it in that way round because of its dimensions but they would have been better to alter the pipework. They could use a male iron to copper into the malleable elbow and copper to an angled gas isolation valve or an elbow and a straight valve.

Hope this helps!
 
It is installed the wrong way round from a design & use point of view and will not shut the gas off as intended (in other words, it is fairly pointless).
That alone is enough reason to have it correctly installed. As it is it will probably isolate the fire but not without allowing a large amount of gas to escape whilst closing it down and replacing the top outer cap & washer in your case, to stop gas escaping. You would really need to turn the gas off (at the meter most likely) to be able to isolate the fire safely.

I suspect they put it in that way round because of its dimensions but they would have been better to alter the pipework. They could use a male iron to copper into the malleable elbow and copper to an angled gas isolation valve or an elbow and a straight valve.

Hope this helps!
Thank you very much for your reply which is very helpful.
 

Similar plumbing topics

  • Locked
You need to get him back to remove so you can...
Replies
5
Views
1K
Ok I think I see what your saying mate, So...
Replies
9
Views
734
I mean you can test with a multi meter on the...
Replies
9
Views
722
Less than 350ppm is acceptable according to...
Replies
2
Views
2K
Experience tells me 10mm won't be enough but...
Replies
5
Views
747
Back
Top