Door off! Checked condense which was clear, checked flue which was clear. Took off burner and checked probes which were fine!
It's gotta be an air flow problem....would a dodgy fan cause this?
Cheers lads
Didn't do a flue gas and it's just dawned on me that it could be an fg problem! Can you adjust the ratio on these piles of poop? Can't see how quickly flicking through manual.
Well worth checking the heat pads are still in place as they can make a noise and also burn hole through the back of the heat exchanger.
I have also come across a couple which make a horrid combustion noise and it was caused by the gas valve. Often fine on full gas but made a noise as it modulated down.
Sorry didn't see you'd checked probes!
Have you checked the flue seals they can be slightly trapped or not put together right. Then they vibrate in the flue when the air is Blown past
Well worth checking the heat pads are still in place as they can make a noise and also burn hole through the back of the heat exchanger.
I have also come across a couple which make a horrid combustion noise and it was caused by the gas valve. Often fine on full gas but made a noise as it modulated down.
Sorry didn't see you'd checked probes!
Have you checked the flue seals they can be slightly trapped or not put together right. Then they vibrate in the flue when the air is Blown past
Thanks for the replies lads....gonna go back with a gas valve and give the heat ex a good clean out....I'd normally associate this fault with blocked condense, but took that out and also had the sump cover off and it was the cleanest isar I have ever seen!
Pipework is fine as with the cover off the heating worked ok. Spoke to ideal they said it's Deffo and airflow prob as it works fine when cover is off.....gonna be a new flue! Which ain't covered on their policy and I don't have one to go back! #dodgedabullet
I cannot believe you didn't fga it? It would have picked this up straight away.
If you check the outer flue also it will tell you if the seals have gone.
Would have taken a lot less time than taking the flue apart.
I cannot believe you didn't fga it? It would have picked this up straight away.
If you check the outer flue also it will tell you if the seals have gone.
Would have taken a lot less time than taking the flue apart.
Flue was over the 3m height I'm allowed to work at the company I work for (only have step ladders, barmy I know)and beings there is no sample point for airflow on a isar....so there! smart ars3.
The test point is on the top of the boiler to the right of the flue. For future reference. ;-)
And for air test. Remove the front cover andand put your fga into the outer flue at the turret. Any co readings and your seals have gone. Your right i am a clever bugger. Lol
The test point is on the top of the boiler to the right of the flue. For future reference. ;-)
And for air test. Remove the front cover andand put your fga into the outer flue at the turret. Any co readings and your seals have gone. Your right i am a clever bugger. Lol