Interested to know if anyone else has had experiance of this. First time I noticed it was on a 60Kw floor standing air heater. We did the entire installation including the gas line from the meter to the unit. On commision gas reading showed a drop accross the gas line of about 4mBar. Then the sweating started. Cheacked my gas pipe sizing calc's about a dozen times, got another enginner to check, all appeared correct. in the end put a test point into the purge point and checked the inlet pressure there. Had a difference of 3.5mBar. i.e. the pressure drop through the gas valve was 3.5Mbar. The pipework was fine about .5Mbar drop.
I have kept my eye out for this ever since and several times been caught with commertial and on occation domestic boilers. ANyone else had this happen to them.