Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Landlords saftey cert gas supply query in the Gas Engineers Forum area at Plumbers Forums

TFGplumbing

Plumbers Arms member
Plumber
Gas Engineer
Messages
997
Hey guys

Just been out to look at x6 boilers that need servicing and land lords saftey checks. And have a question as I've not come across this particular set up before.

So there's x6 boilers located in chalets all with separate gas supplies fed from one G10E meter.
As a domestic engineer can I work on this system?

Thanks
 
Hey guys

Just been out to look at x6 boilers that need servicing and land lords saftey checks. And have a question as I've not come across this particular set up before.

So there's x6 boilers located in chalets all with separate gas supplies fed from one G10E meter.
As a domestic engineer can I work on this system?

Thanks
First question is, is that Meter big enough?
What size are the Boilers?
As far as the Domestic / Commercial question goes.
If the Primary Meter is a U16 or less and the installation is less than 0.035 M cubed including the Meter and the pipework is 35mm bore or less and the OP on the outlet side is no more than 21mb, then yes.
 
First question is, is that Meter big enough? What size are the Boilers?
As far as the Domestic / Commercial question goes.
If the Primary Meter is a U16 or less and the installation is less than 0.035 M cubed including the Meter and the pipework is 35mm bore or less and the OP on the outlet side is no more than 21mb, then yes.
I would be surprised if that meter would do 6 boilers on max rate all at once. Even with 35mm pipe.
 
Aslong as your not tt the meter yes

But I don't agree with it
 

Similar plumbing topics

Whereabouts are you based
Replies
2
Views
1K
the Same position for meter but riser outside...
Replies
3
Views
2K
We've just sorted one of these situations...
Replies
9
Views
1K
  • Locked
Closed as we don’t allowed detailed gas advice...
Replies
24
Views
5K
Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
Back
Top