Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Leaking towel radiator in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

plumb_know

Plumbers Arms member
Plumber
Gas Engineer
Messages
558
Went to a job where customer has had new towel rad and new rad valves fitted, had leak coming from rad tail where it goes into radiator. Customer had bought new rad valve and wanted me to fit them as original plumber away. I thought when rad was fitted maybe they hadn't put tape round thread, so fitted new rad valve and rad tail using loctite and small amount of ls-x. This didn't solve the problem so I believe it must be a faulty radiator, would you guys agree with this?? Also when I was screwing in the radiator tail I could screw it all the way into the radiator, there was not a point where it would stop or become really tight, is this normal as I have never been able to do this on any other radiators??

All replies appreciated
 
i would have used ptfe instead of lsx, around 15 turns then you wouldn't get any leaks
 
Previous plumber used ptfe though and it still leaked, I used to use ptfe but was advised to use loctite as apparently it is better ? What about the tail being able to screw all the way into radiator without stopping? It this normal? It didn't seem to get tight using loctite or ptfe?
 
Previous plumber used ptfe though and it still leaked, I used to use ptfe but was advised to use loctite as apparently it is better ? What about the tail being able to screw all the way into radiator without stopping? It this normal? It didn't seem to get tight using loctite or ptfe?
yes this can happen i have noticed this on some tvrs as well,
just follow the same advice as what others have said, however take notice on how far you first inserted the valve then just dont insert it as far next time. i usualy get to the last thread or two then stop, with no leaks
 
So it's ok that I can screw the rad tail all the way into radiator? Only thing I can't work out is why it is only the one rad tail that is leaking? The other one is fine! Surely both would be leaking as both installed the same?
 
So it's ok that I can screw the rad tail all the way into radiator? Only thing I can't work out is why it is only the one rad tail that is leaking? The other one is fine! Surely both would be leaking as both installed the same?

Could be one slightly oversized female thread but a generous dose of ptfe will solve.
 
Ok cheers for replies I will try with ptfe and some paste and see what happens
 
depending on what valves, your using if they a 3/4 unions try and find some stella rad valves with the rubber seals on the tails they are similar to the air vent and plug sealing method
if the valves are 1/2inch nut and ring type then its lots of tape and boss white im afraid
 
Correct me if I'm wrong but aren't new radiators pressure tested before they leave the factory?

Our highly automated, high speed manufacturing lines feature pressure testing to 10.5 bar to assure weld integrity and a thorough leak testing regime, followed by a four stage inspection process.
^ From Stelrad's website.
 
Last edited:
Correct me if I'm wrong but aren't new radiators pressure tested before they leave the factory?


^ From Stelrad's website.

I suppose it depends on how they are tested. If the test rig is set up like the old engine compression testers with a rubber conical adapter then an oversize thread would pass as the seal could still be made and the radiator body withstand the test pressure.
 
I have noticed on some rad valves the lock shield tail thread doesn't go tight. If you have another set of valves try the tail for the TRV as they seem to fit better, plus as previously said lots of PTFE. ( found this with Plumb centre Bulldog valves).
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Finally got it to seal - ptfe paste to fill...
Replies
12
Views
4K
Size of bathroom 230cm x 210cm Height 230cm...
Replies
0
Views
577
  • Question
https://www.NoLinkingToThis/p/fernox-ls-x-leak-sea...
Replies
6
Views
2K
  • Question
I do not believe that the end cap doesn't come...
Replies
7
Views
586
  • Question
Thanks - has done the job nicely. Most...
Replies
3
Views
906
Back
Top