Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Less heat in a condensing boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
G

Gerard17

Did any1 no that a a normal gas boiler heats a rad 30% more than on a condensing boiler. Has any1 ever fitted a new boiler like a combi swap an the customer says the house isn't has hot?
 
Did any1 no that a a normal gas boiler heats a rad 30% more than on a condensing boiler. Has any1 ever fitted a new boiler like a combi swap an the customer says the house isn't has hot?
no,never have had that issue
 
I've had it once or twice but just think there being silly as there not complaining or anything but when I went on that worcester course 1 of the worcester fellas (who knew his stuff) was telling me about the diffrence between them. I couldn't work it out as the water in the rad can still get up to 80 degrees if u wanted it to
 
Properly sized boiler??? 30si in a 2 bed, 1 bath, 6 rad system don't no what calculations u do but I would say that was more that adequate
 
With the lower flow temps the cond boilers like to run with the output of the radiators does drop, though as mentioned above, turn up boiler stat to max and it'll be fine, not condensing but belting the heat out.
 
As long as the return stays below 55 degs it will condense!

i think the OP is getting mixed up when the rads manufactures changed the delta t calcs, from 60 to 50
 
So if the return is above 50 degrees the boiler doesn't condense
 
So if the return is above 50 degrees the boiler doesn't condense
Correct 55 not 50 ....hence on WB,Vaillants etc, max flow is 75 degs ( unless you override it) balance to get your 20 deg diff, return stays at 55 degs so boiler stays in condensing mode, until SYTEM cannot dissipate any more heat evenafter modulating down, then diff drops, return temp goes up, boiler stops condensing...
 
A properly sized boiler AND RADIATORS means that should never happened.

The properly tuned condensing boiler STARTS condensing at ~55 degrees or so,
Than, the LOWER the return T the MORE% of the H2O vapor it condenses (an the more fuel(money)% it can save).
To get MOST of it, DOUBLING radiator size/output is strongly recommended.
(versus typical old system). + room thermostat.
Usually it is mentioned somewhere in small print in the boiler install manual, (like for Junkers).
There is really very little gain from the condensing boiler on a tiny piping hot radiatos... (Unless you blow a fan on each of them (like on the PC's CPU cooler))

And the usually way undersized radiators of the typical UK installation are rarely mentioned... (Unlike the boiler size).

I've lived in 10 houses for the last ~10 years, and only the St. John's college had a properly sized radiators for the condensing boiler...

PS: I would not be surprized if the UK government adds a regulation in a future (in a bit to get higher energy efficiency/insulation), that the house should reach at least 18 degrees, when the outside temp is 0, and the maximum flow temp is 40-45 degrees (return 30-25 degrees). I've seen few houses with the 100+ years old systems perfectkly functioning (and crast iron/bronze radiators), which were meeting this flow temperature requirements.
 
Status
Not open for further replies.

Similar plumbing topics

R
Wb 4000 recently installed, and just balanced...
Replies
0
Views
530
Return temperature
R
You've already spent thousands on a new boiler...
Replies
2
Views
960
Below is a sizing chart based on a heat loss...
Replies
1
Views
797
Thanks to @ShaunCorbs and @cjg for the helpful...
Replies
7
Views
808
There is 6 pipes under the boiler and one goes...
Replies
19
Views
1K
Back
Top