Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Loft conversion en-suite waste length help in the Plumbing Jobs | The Job-board area at Plumbers Forums

Messages
6
Evening All

Have had some very useful help so far in reading this site so now time to ask my first question.

Please be gentle

We are in the process of a loft conversion that has an en-suite incorporated we had some basic plans done by an architect to inculude this but as we come to plumbing time we are struggling with the maximum waste pipe length arrangement.

I understand waste pipe at 40mm is a max run of 3m I need to run about 7.5 to get to soil drop.

Is it possible to run sink and shower waste at 40mm at 7.5m if I include an AAV? Fall is not an issue as new floor is way above our exit void into small back loft which is not part of conversion.

Running a new soil pipe for loo but on other side of wall, fall tricky to get 40mm into due to brick obstacles

Thanks in advance
 
I'd run it in 2" but where are you getting your max run measurements from? I wasn't aware there was a max run for shower wastes.
 
Why did you think there was no max??
Because it's something I've never come accross before. Even now when reading part H of the building regs I can't find anything specific to shower and bath wastes, the only appliances it mentions are toilets, bidets, basins and urinals, and from what I can tell that's on unventilated systems. Mcalpine state there is no max length for baths or showers but I guess that's not an official document. I've always gone off the basis of keeping my runs as short as possible which adequate fall but I'll admit I have ran shower wastes longer than 3m when necessary.

Screenshot_20190130-223200.png
 
Ah. Well there is something about sprinkler taps on basins that don't have plugs so I see the logic.

If the shower has no plug, then the trailing discharge will prevent the trap from being left dry, even if siphonage occurs. But if there is a sink (do you mean basin?) also, then this is not relevant to this situation as the basin would indeed suffer from a siphonage situation.

Not convinced AAVs or waterless or resealing traps are acceptable in a new-build situation and I think the 'correct' way is secondary venting, but perhaps it's just a case of having to wait for the Approved Documents to catch up with modern practices.
 
Last edited:

Similar plumbing topics

Should have added in, naturally there will be...
Replies
3
Views
1K
Thank you
Replies
5
Views
2K
Thank you for your reply... where can I find...
Replies
3
Views
4K
  • Question
Over that distance, I don't even think 50mm...
Replies
3
Views
6K
run them below and through the wall ?
Replies
3
Views
2K
Back
Top