Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Log Burner Boiler pipework in the Boilers area at Plumbers Forums

Status
Not open for further replies.
T

tim

Hi All
Have two questions first is can i use 22mm pipe on heating side which is pumped and 28mm pipe on the gravity hot water and secondly how far does the copper from the boiler need to be before i can convert to plastic.
Cheers for a very informative site.

Tim
 
Yes 22mm is if on heating side and 28mm on gravity hit water but would not use plastic anywhere on a wood burner
 
Hi5
Thanks for your advice but can you tell me why you would not use plastic pipe as my existing
heating system is about 90% plastic already.
Cheers
Tim
 
... can you tell me why you would not use plastic pipe as my existing heating system is about 90% plastic already...

5. Can I connect Speedfit Pipe and Fittings directly to a central heating boiler?

No. Although most modern boilers have a high limit thermostat, residual heat can be conducted by the heat exchanger. Unless the boiler manufacturer states otherwise, a minimum of 1 metre run of pipe from the boiler casing should be copper. This recommendation includes the cold water mains supply to a combi boiler.
Speedfit Products should not be fitted to a back boiler or other uncontrolled heat source.

from John Guest Speedfit Frequently Asked Questions

Having said this, the uncontrolled heat source comment doesn't seem to appear in their latest technical advice, so maybe I'm (we're) out of date.
 
Status
Not open for further replies.

Similar plumbing topics

What I mean is that because everything works...
Replies
3
Views
733
Very informative...........thx🙄
Replies
3
Views
589
The boiler is just responding by limiting the...
Replies
8
Views
1K
I should have said "S-plan plus", of course!
Replies
17
Views
2K
Back
Top