S
superhands
Hi,
Currently on a job where the hot water tank is in the basement with a 20 meter run to the loft then drops to the bathrooms and takes at least 3 mins for the hot water to come through so trying to look at a way of fixing this. I have thought about a secondary circulation but I'm not that keen on the idea.
I think maybe one of the problems along with the distance is that the pipe size is 1/14" for the first 10 meters then reduces down to 1" then finally reduces to 22mm to drop into the bathrooms.
Would it come through significantly quicker if the supply from the cylinder was run in 22mm all the way, and also would the pipe be large enough for 2 bathrooms(bath/shower cubicle in one just shower in the other), I'm kinda thinking it should be 28mm to supply both.
Would appreciate any thoughts on this
Thanks
Currently on a job where the hot water tank is in the basement with a 20 meter run to the loft then drops to the bathrooms and takes at least 3 mins for the hot water to come through so trying to look at a way of fixing this. I have thought about a secondary circulation but I'm not that keen on the idea.
I think maybe one of the problems along with the distance is that the pipe size is 1/14" for the first 10 meters then reduces down to 1" then finally reduces to 22mm to drop into the bathrooms.
Would it come through significantly quicker if the supply from the cylinder was run in 22mm all the way, and also would the pipe be large enough for 2 bathrooms(bath/shower cubicle in one just shower in the other), I'm kinda thinking it should be 28mm to supply both.
Would appreciate any thoughts on this
Thanks