Hi guys an update....
Been there yesterday, and had a good look around ..
Like I said B4 it's a Gravity system- Baxi 30HE, Alpha (digi pump on 2), 2X 2 port valves,
(1050) HWC-set to 65~c, Big OLD CWSC and F+E tank, 12 rads.
2 bathrooms- towel rails-one on AND one-OFF!- guy said bathroom was getting too hot, so he shut the valves..here's the problem me thinks..he's shut the by-pass, SO this could be why his boiler locks out when he turns the room stat DOWN-YES?
But now the lockshields-fairly crudded won't open.. well i didn't want to try very hard cuz it was just a fault finding mission. BUT also while I was there, the F+E tank vent started spouting hot water... IS THIS ALSO CUZ THE BY-PASS SHUT_YES??
The 2 TPV's seem to be operating but not quite sure how to test if there's a fault.
Had HW on one valve opened, had CH+HW on other valve opened, they also had resistance when closed... Was this the right way to check?
Anyway will appreciate your advice.....
-----Can you get a decent shower off a gravity system, the head is about 4-6foot, CWSC is raised. At the mo' they got a shower mixer bath tap and ...well... it's not going to work!! EVER! I think he's looking at electric or power shwr ?
Lastly, the thing with the pump was a pie in the sky, it's not connected!!!
I do like a bit of problem solving, with a little help from my 'friends' ...get me rusty bits going again...
Thanks for listening :1eye:
Been there yesterday, and had a good look around ..
Like I said B4 it's a Gravity system- Baxi 30HE, Alpha (digi pump on 2), 2X 2 port valves,
(1050) HWC-set to 65~c, Big OLD CWSC and F+E tank, 12 rads.
2 bathrooms- towel rails-one on AND one-OFF!- guy said bathroom was getting too hot, so he shut the valves..here's the problem me thinks..he's shut the by-pass, SO this could be why his boiler locks out when he turns the room stat DOWN-YES?
But now the lockshields-fairly crudded won't open.. well i didn't want to try very hard cuz it was just a fault finding mission. BUT also while I was there, the F+E tank vent started spouting hot water... IS THIS ALSO CUZ THE BY-PASS SHUT_YES??
Alpha pump at boiler does turn off when I turned stat down after about 2 min-OK...? So the overun is wired in ?To me it sounds like a 2 port valve shutting off and bypass not open enough or not there but could also could be pump overun not wired in.
The 2 TPV's seem to be operating but not quite sure how to test if there's a fault.
Had HW on one valve opened, had CH+HW on other valve opened, they also had resistance when closed... Was this the right way to check?
Anyway will appreciate your advice.....
-----Can you get a decent shower off a gravity system, the head is about 4-6foot, CWSC is raised. At the mo' they got a shower mixer bath tap and ...well... it's not going to work!! EVER! I think he's looking at electric or power shwr ?
Lastly, the thing with the pump was a pie in the sky, it's not connected!!!
I do like a bit of problem solving, with a little help from my 'friends' ...get me rusty bits going again...
Thanks for listening :1eye: