Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Low head pressure tmv suitable for unbalance supplies. in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
S

Sharp Point

Got a 'doc m' pack to fit soon in a working mens club, the hot is being supplied via a wall hung water heater, the type being fed by a little cistern above, the height of the water level is approx 2m above floor level and the tmv for the new wash basin will be approx 1.5m below water level. and to add another spanner in the works, the cold is off cold mains. Is there a tmv on the market that will work with this set up.


cheers
 
no the only way is prv down to same out pressure as r25
 
Even with prv it probably won't work you have 0.15 bar hot water don't think you can get cold through prv down enough, I have just taken out exactly the same set up from community centre because all they ever got was cold water.
 
Even with prv it probably won't work you have 0.15 bar hot water don't think you can get cold through prv down enough, I have just taken out exactly the same set up from community centre because all they ever got was cold water.

they do work thats all one comp have been doing round here, the only other option is use of an ariston mains water heater
 
I'm taking a brand new one of these out next week! Your welcome to it mate!
image.jpg
 
A spark wired it in with a 3 pin plug about 300mm away and below the basin!!
 
Thanks for the replies, I knew it'd be touch and go as to whether a low head/ unbalanced tmv would be possible. I have notified the builder, that'd he's probably going to have to get an unvented set up.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Yeah all buried so not an easy leak fix.
Replies
7
Views
1K
  • Question
If you have a pressure gauge on the pump...
Replies
8
Views
845
  • Question
You are confusing pressure and flow. Your...
Replies
6
Views
4K
Replies
1
Views
970
    • Like
  • Question
I was asking Philbutton about his problem.
Replies
9
Views
2K
Back
Top