I got called out to a worcester bosch greenstar 37cdi combi the other day. Locking out, flashing EA. Put the u gauge on, fire it up on max rate the inlet pressure was dropping to 0mb and locking out. Test at meter and got 20mb as it ramped up to max rate before locking out. Took the gas valve out and the filter was full of swarf from old barrel pipe but the whole outlet side of the meter is copper. I cleaned it all out, blew some gas through the open ended pipe and more swarf shot out. Put the valve back in, tested again. Now getting 2mb at max rate and still locking out. Out comes the gas valve again, filter blocked up again. Cleaned it out, blew more gas through the open pipe. Put back together, now getting 3.5mb at full rate and locking out. Take it out again, filter not too bad but clean anyway. put back together and now getting 6mb on max rate and the boiler isnt locking out remarkably.
I dont really know what to do, I have a feeling the gas valve has been damaged and is a bit blocked internally past the filter still as the last time it came out there was hardly any swarf. Will the gas transporter do anything about the main bringing in a load of crap? Do I just replace the gas valve? Or do I replace it and run a new supply from the meter incase there is any blockage of swarf along the way which is causing the low pressure?
I dont really know what to do, I have a feeling the gas valve has been damaged and is a bit blocked internally past the filter still as the last time it came out there was hardly any swarf. Will the gas transporter do anything about the main bringing in a load of crap? Do I just replace the gas valve? Or do I replace it and run a new supply from the meter incase there is any blockage of swarf along the way which is causing the low pressure?