Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Low working pressure at boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
P

Plumber Direct

Hi to all,




I'm a gas engineer having a bit of a nightmare on a job, we have installed 37kw boiler. We are getting 12mb working pressure at boiler and 19mb at meter. original pipe running from meter was in 22mm so I thought pipe sizing issues, we have now installed a 28mm run from meter to a 22mm pipe which is around a meter long that connect to boiler. Still getting the same working pressure 12mb , I have tried everything then I thought it was boilers gas valve. Vaillant engineer turn up and he said there was nothing wrong but still changed the valve and we still have the same working pressure. I'll really like to hear any opinions would really appreciate thank you
 
This is a public forum so we can't offer GS advice.
 
Last edited by a moderator:
Ecotec 837 ? But wrong forum
 
Last edited by a moderator:
Hi thanks for you replies, sorry didn't know how the forum works new to this. Not to sure how to repost on gs only
 
you need to post your gsr number to one of the mods and get let in to the closed forum to get any gas advice on here
 
Status
Not open for further replies.

Similar plumbing topics

Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
The boiler is just responding by limiting the...
Replies
8
Views
1K
A bit late but what were the test results, did...
Replies
10
Views
3K
What the easiest way to find why my boiler is...
Replies
0
Views
526
B
    • Like
Did you find a resolution to your problem? We...
Replies
3
Views
1K
Back
Top