Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Lp20rf not firing up cdi35 worcester bosch boiler in the Boilers area at Plumbers Forums

Messages
3
I recently moved into a flat with a Worcester Bosch CDi 35 Compact (or Classic System maybe?) and the thermostat on the boiler was broken (the thermostat was visibly damaged). I replaced it with a Drayton LP20RF receiver and thermostat. The boiler guy came round once other work was completed to reconnect the gas and sign off the boiler - he said it all looked ok, but that was before I had got the thermostat connected and running. I have connected everything up now, and although the thermostat is requesting heat and the LP20RF unit is responding, the boiler never actually produced hot water for the radiators.

I have spoken to Drayton and they think the thermostat and receiver are working fine, and the boiler can make hot water for the taps, it just never seems to interpret the signal to come on correctly for central heating. Therefore I thought maybe I needed to do some rewiring inside it - I opened it up and I think I need to do something with the switched live and live return terminals, but I don't know where the signal wires from the thermostat (connected with a ribbon) are coming out...

Is it clear what I need to do, looking at the attached photo? I don't think I can afford the boiler repair guy coming out again (certainly not this month!) and it is getting really cold now, so I could definitely do with some central heating!
 

Attachments

  • IMG_20221120_145912.jpg
    IMG_20221120_145912.jpg
    298.6 KB · Views: 42
:D he never reinstalled the link that you require should link ls to lr
 
Yep
 
It worked! Brilliant and amazing! This has made such a huge difference to my quality of life! It was looking to be a very cold Christmas, what with callout charges - Thank you so much! One small wire for the boiler, one giant leap for me! This is wonderful! :D
 

Similar plumbing topics

Reply was much appreciated, thank you.
Replies
4
Views
861
Or elec bills as it would be running...
Replies
9
Views
566
Apologies for not attaching photos but many...
Replies
4
Views
680
W
pcb issue so gas safe engy required sorry to say
Replies
1
Views
701
Have you tried turning it off and on again ?
Replies
2
Views
1K
Back
Top