Hi Guys,
Got a Main Combi 24 HE which is stuck on flame failure. Customer had a gas leak on the gas run which was repaired, after this the customer turned the boiler on from the spur and the boiler is was stuck on flame failure which flashes slowly.
When hot water demand is given the pin hits the microswitch but boiler does not go through sequence. When heating demand is given the pin does not push out to hit microswitch, however I made manual contact to the heating switch and the boiler sparks but does not ignite and locks out.
I have checked pump by removing the bleed scre and pump is spinning, checked gas valve and getting 23mbar on p1.
Can anyone give me further guidance as customer is saying it only started with flame failure after gas leak was fixed. All gas isolation valves are open.
Thanks