Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Major issues with New Boiler system and radiators in the Boilers area at Plumbers Forums

Messages
1
Just had new Worcester Greenstar 8000 Lite Boiler and all radiators replaced.



We upgraded to a combi Boiler.

Had issues during and now after installation.

Radiators are based over three floors with

Four on the ground floor, Four on the First floor and three on the top floor.

Issues range from several radiator hot a top and cold towards the bottom of the radiator.

Radiator on the first floor range from one radiator not working at all to hardly any heat coming out of the other three.

Three of the radiators, in flow pipe hot but cold on the return pipe. One of the radiators flow in pipe and return pipe is cold this radiator pipe work is connected to one of the other radiators.

Several of the radiators in the system have the heat coming in on the TRV pipe and others on the Lock shield Valve pipe.

Had a leak on the pipe work in the cellar during installation and was told to re pressurise the system but the bar pressure kept falling and then went and checked pipe work able to be seen and found leak as noted about and had to turn the system off until if was fixed after the weekend.

Has air gone into the Heating system? Tried bleeding all radiators but no air in the top of the radiator. Does the system need topping up with Inhibitor after leak? No help or no interest from the Heating engineering about making sure the system was working correctly before leaving the Job.

All radiators have new TRV fitted.

Any advice or help would be gratefully received on what areas could be causing issues with the New Heating System and radiators.





 
The system needs to be balanced. The residual pump head might not be enough to generate flow though and I can’t see a chart displaying the details. It is possible the pump within the boiler isn’t man enough to cope with the system demand, in which case the system requires some sort of separation and an additional pump.
 
The Boiler/system should have been commissioned properly by the installer but you can check out a few items yourself.

System should have been flushed through before installation of new rads and a magnetic filter installed to protect the Boiler Hx.
Boiler (assumed on ground floor) pressure should be 1.5 bar when cold to allow for 3 floors.
Have you tried it on each floor only?
TRV manufacturer?

I think these boilers may come with the circ pump set to 2.5M head (setting 3) which may be too low for your system, would suggest set to 4M (setting 6), you should be able to access this yourself from the boiler menu and check/reset it.

1648793385628.png
 

Similar plumbing topics

S
Morning all, I have a Worcester Bosch 8000...
Replies
0
Views
656
Simon from Watford
S
You’re 200 miles away - he is there. You’re...
Replies
3
Views
587
Turned out to be a dirty flame eye inside the...
Replies
8
Views
704
Thanks :) . A happy new year to you!
Replies
23
Views
1K
Back
Top