frustrateduser
In short, can anyone tell me what max load of a U6 meter is, is it 65KW or 6m3/hr.
I am looking at two boilers at 30kw and 24kw, plus one gas cook at 9kw, total usage is 63KW/hr which is within the 65KW.
However, if I look at the gas flow rate, 30kw boiler at 3.4m3/hr and 24 KW at 2.59m3/hr. Just two boilers already reach 6m3/hr. Does that mean I need to have a U16 meter in order to have a gas cook.
Many thanks,
I am looking at two boilers at 30kw and 24kw, plus one gas cook at 9kw, total usage is 63KW/hr which is within the 65KW.
However, if I look at the gas flow rate, 30kw boiler at 3.4m3/hr and 24 KW at 2.59m3/hr. Just two boilers already reach 6m3/hr. Does that mean I need to have a U16 meter in order to have a gas cook.
Many thanks,