Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Measuring Working Pressure at the Meter in the Gaining Plumbing Experience area at Plumbers Forums

stratplus

Plumbers Arms member
Plumber
Gas Engineer
Messages
953
Who, when you take a working pressure at the meter in a property with multi appliances (or boiler and cooker) record the measurement on a cp12 with all the appliances working?
Or do you just have the appliance with the largest load on?
 
i do all as the gas pipe supplies all and each affect each other
 
But you’re only testing the meter regulator.

Yes but you need to know the reg is working correctly

If your doing a working at the meter your also doing a working at the appliance
 
Yes but you need to know the reg is working correctly

If your doing a working at the meter your also doing a working at the appliance
Yes but you need to know the reg is working correctly

If your doing a working at the meter your also doing a working at the appliance
Yes but you need to know the reg is working correctly

If your doing a working at the meter your also doing a working at the appliance
As an example scenario:
Property has a combi boiler and cooker
Working pressure at METER with boiler in service mode and 3 rings on cooker 18.5mb ( below 19mb)
Working pressure at METER boiler only (service mode) 19mb (within tolerance).
Working pressure at BOILER within 1mb tolerance so no issue with pipe sizing.

Would you call this into the grid to increase pressure at regulator?
I know engineers who only have the boiler on when doing working pressure at the meter so in the above scenario would pass this and walk away.
 
No I wouldn't if it went down to 14mbar I would then
 

Similar plumbing topics

Ok I think I see what your saying mate, So...
Replies
9
Views
731
  • Question
I had a chattering float valve in the loft...
Replies
2
Views
323
  • Question
Sounds to me that the 15mm pipe that you are...
Replies
14
Views
1K
Essaboy
E
Thank you for the replies. I had another...
Replies
4
Views
836
A
  • Question
Thanks for your reply - softener is brand new...
Replies
4
Views
1K
Azonic
A
Back
Top