Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Megaflo not heating enough water in the Bathroom Advice area at Plumbers Forums

Messages
3
Hi, I have a megaflo used for water (heating is electric), and for some reason I have found in the winter that there is not enough hot water, it only lasts for one shower. This doesn't happen in the summer for reason.

Can anyone suggest some solutions, I have checked the temperature on the thermostat and it seems fine. Would like to learn more before calling an engineer.

Thanls
 
Generally (not always) the MegaFlo cyclinder will have two immersion heaters.

The lower one heats the entire cylinder and is often connected to a cheap rate night time tariff such as Economy 7.

The upper one heats about the top third of the cylinder, and is used to boost the hot water if it runs out. Usually good for one long(ish) and possibly one short shower. Usually connected to normal rate electricity supply.

If you have the above set up, ensure that both immersion heaters are switched on. If only the top one is on, you might get enough hot in summer when the incoming cold is a bit warmer, but not enough in winter.
 
Hi, I have a megaflo used for water (heating is electric), and for some reason I have found in the winter that there is not enough hot water, it only lasts for one shower. This doesn't happen in the summer for reason.

Can anyone suggest some solutions, I have checked the temperature on the thermostat and it seems fine. Would like to learn more before calling an engineer.

Thanls

How have you checked the thermostat ? If you have done it by “ clicking it “ like most , its not accurate.
Post a pic of the stat , most of them are garbage.
 
Measure how many litres per minute your shower delivers by timing how long it takes to fill a known volume, such as a measuring jug or kettle.

What model of Megagflo do you have?
 
The reason for the winter / summer difference is the temperature of the incoming water, the 3kW immersions has to do a lot more work in the winter when it is cold, so you get a quicker heat up.

I bet you have both elements switched on but the bottom one has failed.

To work on these unvented water heaters the Law (Building Reg's) states you must hold a Part G (unvented hot water) ticket.
Please call in a pro who is qualified (ask to see proof), these systems can be a danger if not done correctly
 
The reason for the winter / summer difference is the temperature of the incoming water, the 3kW immersions has to do a lot more work in the winter when it is cold, so you get a quicker heat up.

I bet you have both elements switched on but the bottom one has failed.

To work on these unvented water heaters the Law (Building Reg's) states you must hold a Part G (unvented hot water) ticket.
Please call in a pro who is qualified (ask to see proof), these systems can be a danger if not done correctly


Thanks, you were right about the thermostat both seem to have blown, the upper one is holding on for dear life but needs changing.

It hasn't been serviced in a while either so the engineer said it may be worth descaling it too. He has quoted me £200 to change both thermostats and descale. Does this seem reasonable?
 
How have you checked the thermostat ? If you have done it by “ clicking it “ like most , its not accurate.
Post a pic of the stat , most of them are garbage.

20190123_211327.jpg


20190123_205514.jpg
 
The other thing to keep in mind is the ratio of hot to cold being used. In Summer, the incoming water supply is warmer so you require less hot water to achieve a comfortable 40 degree shower. In winter, you will require more hot water, so it will run out faster.

You should ensure the water is being heated to 60 degrees plus.
 
[QUOTE="Saif, post: 1023148, member: 101427"
It hasn't been serviced in a while either so the engineer said it may be worth descaling it too. He has quoted me £200 to change both thermostats and descale. Does this seem reasonable?[/QUOTE]
Yes very. - I charge £200 just for the repair (plus parts), more if it requires a descale but these are London prices with London costs, it is soon going to cost me £12.50 on top of the £11.50 just to drive in, let alone the parking £4+ per hour (2 hours to travel 17 miles each way).
 

Similar plumbing topics

  • Question
Are these supposed to be at mains voltage or...
Replies
7
Views
757
I don't believe moving the manual lever over...
Replies
5
Views
505
  • Question
I think this is the most likely solution...
Replies
10
Views
1K
M
Isolate and drain boiler. Pump up expansion...
Replies
1
Views
729
Thermostat changed... With the new one, it...
2
Replies
38
Views
1K