Morning all quick question

I was always of the impression that a meter piped on double anacondas was wrong. Just come across this but gas safe have said its fine as long as it's on A meter bar.

I don't really mind either way as I've already found enough on this system to condemn the boiler but I'm just curious for my own information

Is this right cheers
 
As long as its bracketed and secure then its just ncs. If not bracketed, i believe there needs to be minimum 600mm of rigid pipework which is clipped correctly
 
Been a recent update. Used to be NCS if two pliable connections used on semi-concealed installation.
Now it is allowable if meter secured to bracket and meter outlet adapter is used to restrain meter.
 
Thanks all. Must've missed that one
 