Hi, I had a Drayton ma1 mid position actuator recently installed as central heating had stopped working. Now my heating and hot water will not come on at the same time (with timed settings) and I have been advised that my thermostat is not working which is causing the problem (from the emergency plumber that had come out). I’m slightly confused as surely if I manually turn my central heating on and the hot water is working then the ma1 should move to the mid position which it does not.. any advice would be greatly appreciated.
 
Maybe he means the room stat?, have you tried turning this up?, if its the old rotary type then you should hear a click from it each time you turn it up/down past the actual room temperature.
Does the CH come on if selected only?.
 
Hi the plumber did say the room stat and I am happy to replace. My confusion is more over the fact that if I turn the heating on manually my hot water and heating don’t work together as the actuator does not move to the mid position...and the actuator is new?
 
Don't know, if the stat has a rotary selector turn it up and down then up again, if your hear a click each time it's unlikely to be the stat and probably a wiring fault. Can you put it in manual, turn up the stat, turn off the HW and see does the valve move fully across to the other side, port A I think. You might post a pic of the room stat.
 
If neither heating or water come on when instructed to do so by the controller either the home is warm enough AND the hot water tank is full of hot water OR you have a wiring problem

its unlikely that both the room stat and the tank stat have both failed so getting somebody competent to check our the heating wiring it the next step forward imho
 
oops yes.

OP is your room stat programmable?
No it’s an old one (pic below). Thanks for your help with this..
F757C4C2-15FF-414F-A29A-EB216A655E36.jpeg
 
One thing that puzzles me slightly: who replaced the mid pos valve? If it was the emergency plumber - did you pay him directly or via a scheme? Either way, why not get them back? If you’re getting heating independently and hot water independently then I’d suspect the mid position valve wiring, not the room stat.
 
To be short, if you can obtain water without heating and you can also obtain heating without water, but not the both together, then it would be really interesting to know how this can possibly be a thermostat fault. To be frank, the company could prove the fault is in the thermostat within 10 minutes if they know even basic electrics.

Please check the new valve says "mid position" and not "diverter" on it. A diverter valve will not stop in the middle and will give you heat OR hot water but not both at the same time, usually giving priority to hot water: have they fitted the wrong type?

Plus, as other have asked, can you get the room thermostat to click on and off? Without knowing that answer, it really isn't worth us speculating further.
 
Please check the new valve says "mid position" and not "diverter" on it. A diverter valve will not stop in the middle and will give you heat OR hot water but not both at the same time, usually giving priority to hot water: have they fitted the wrong type?

This is a goldmine point. Op has said it’s a MA1, that said it could be a ZA1 which is the diverter
 

Similar plumbing topics

  • Question
Prob using the blue core from the cylinder...
Replies
9
Views
2K
G
  • Question
Dodgy contacts on old programmers or cylinder...
Replies
5
Views
2K
  • Question
This one should do it bud
Replies
4
Views
4K
  • Question
Might be worth putting weight in the tray and...
Replies
9
Views
677
  • Question
You could, but it could also be gears...
Replies
3
Views
1K
Deleted member 120897
D
Back
Top