I've got the manual but all I can do is give you some info from it.
This fire ceased production on the 01/09/1987
There are three different serial numbers, which one have you got?
Homeflame Unigas (From S/N 10G000) ANT BRN/BRN/BL
Homeflame Unigas (from S/N 10E000)
Homeflame Unigas (Upto S/N 99D999)
Here is some data from the last one listed.
Heat Input - Settings (4) 4.69kw
(3) 4.46kw
(2) 2.21kw
(1) 0.88kw
Heat Output -Settings (4) 3.33kw
(3) 3.17kw
(2) 1.34kw
(1) 0.51kw
Pressure test point on main supply to burner
Setting pressure 17.8mbar (Hot) and 17.4mbar (cold) at setting 4
There is no adjustment for gas rate and aeration is fixed.
Spark gap - 3.5 plus minus 0.5mm
I hope this info helps, if you need any more info then just ask, no problem.
Sent from my iPad using Tapatalk HD