Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Mixed diameter Flow & Returns in the UK Plumbers Forums area at Plumbers Forums

Messages
1
Hi all.

Recently had a new combi installed (Glow-worm Energy 30kw) in a new location (moved from upstairs to down). The flow and returns now leave the boiler in 22mm (for approx 1m), then drop to 15mm to feed the first two upstairs radiators, which are closest to the new location. This then links to the original 22mm running through the centre of the house where the other rads are tee'd off on 15mm. So in essence, the flow and returns go 22mm-15mm-22mm-15mm. I've attached a rough diagram (single pipes just for clarity).

I'm struggling to balance the system and the furthest rads (most used) are taking a long time to heat, and even then the output isn't great. It is feasible to run 22mm back to the boiler from the centre of the house, although will involve lifting a floorboards in a recently decorated room. On install of the new boiler, this would have been easy as there wasn't a plasterboard ceiling at the time. But as it wasn't done, I didn't question it thinking that modern boilers can handle this.

My questions are, is this current configuration acceptable or am I always going to have problems? Does it risk damaging the boiler by overworking the pump or is it less efficient? Is balancing always going to be difficult with the mixed diameter piping?

Many thanks for your time.
 

Attachments

  • Heating System Diagram.png
    Heating System Diagram.png
    18.8 KB · Views: 36
Nope needs to be 22mm as you will have flow problems and will shorten the life of the boiler bad install from the people who fitted said boiler
 
Here are the numbers to show that a significant length of 15 mm pipe is unsuitable due to excessive pressure loss at the required flow. According to the Installation and maintenance instructions Energy7 30c:
  • Nominal water flow (ΔT = 20 K) is 1,094 l/h
  • Nominal water flow (ΔT = 30 K) is 729 l/h
  • The flow rate-pressure curves for the pump at maximum speed show an available pressure of about about 17 kPa (170 mbar) at 1,094 l/h and about 35 kPa (350 mbar) at 729 l/h.
Tables of pressure loss are here:
https://www.pegleryorkshire.co.uk/MEDIA/Downloads/CC_004/82498733_Pressure_Loss_Tables.pdf
  • At 0.3 l/s (1,094 l/h) the pressure loss is 51.8 mbar/m in 15 mm copper pipe and 6.5 mbar/m in 22 mm copper pipe.
  • At 0.2 l/s (729 l/h) the pressure loss is 25.1 mbar/m in 15 mm copper pipe and 3.2 mbar/m in 22 mm copper pipe.
 
Here are the numbers to show that a significant length of 15 mm pipe is unsuitable due to excessive pressure loss at the required flow. According to the Installation and maintenance instructions Energy7 30c:
  • Nominal water flow (ΔT = 20 K) is 1,094 l/h
  • Nominal water flow (ΔT = 30 K) is 729 l/h
  • The flow rate-pressure curves for the pump at maximum speed show an available pressure of about about 17 kPa (170 mbar) at 1,094 l/h and about 35 kPa (350 mbar) at 729 l/h.

  • At 0.3 l/s (1,094 l/h) the pressure loss is 51.8 mbar/m in 15 mm copper pipe and 6.5 mbar/m in 22 mm copper pipe.
  • At 0.2 l/s (729 l/h) the pressure loss is 25.1 mbar/m in 15 mm copper pipe and 3.2 mbar/m in 22 mm copper pipe.

If I understand this correctly, what you're saying is that for the 0.2 L/s scenario (as example), you could only have:
  • 14m of pipe in 15mm
  • 110m using 22mm
Is that correct?

Thanks,
Pozer
 

Similar plumbing topics

  • Question
Same as why most heat only come with 15mm gas...
2
Replies
26
Views
2K
Pipework looks fine maybe try balancing the rads ?