Got a 2 and half year old EcoTec Pro 24 showing F75 on CH demand. DHW is fine.

Pressure differential sensor? If so where is it? Never worked on something so new!
 
Pressure sensor bottom left of hydroblock. Kit is a bit of pipe to lift sensor up 10mm to stop air lock. Quick fix blow off prv to clear air. Kit is about £5
 
Read alot on google about this. Sounds like a pain... Going there tomorrow, will try the blowoff, Il get a replacement sensor to take with me. Is there any info on here about the config settings?
 
Read alot on google about this. Sounds like a pain... Going there tomorrow, will try the blowoff, Il get a replacement sensor to take with me. Is there any info on here about the config settings?

It's a real easy fix.
 
Drain the boiler using the drain off underneath, remove and clean the pressure sensor and re-fit. It'll be full of rubbish. If it keeps happening then the F75 kit will help, it changes the flow pipe from the heat ex so the pressure sensor is right by the heat ex instead of on the manifold and comes with a loom extension.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Have you got any updates on this?
Replies
1
Views
1K
  • Locked
Will be surprised if you ca not clean it out...
Replies
7
Views
110
  • Question
I think 2.7LPM is the minimum requireed so...
Replies
4
Views
364
That is true - however with Vaillant...
Replies
4
Views
964
  • Question
Hi I'm dealing with Vaillant Ecotec 824 R1 in...
Replies
0
Views
654
Back
Top