just serviced my own boiler,a main 24he 4 year old,out of the 140+ plus of these i have fitted why does the gas valve have to fail on mine?sods law, pressure should be 10.2 mb mine was chucking out 16mb no amount of adjusting would bring it down,so i have just had to fit a new gasvalve as i have so many of this boiler fitted i have one of every thing in stock this valve cost me £47+vat so not to bad
 