The pipe from my gas meter to my Worcester combi boiler is 22mm. It is 16m long and has 6 right angle bends after the meter.

Does anyone know the formula for calculating pressure fall from coming into themeter at 21mb to arriving at the boiler?
 
I thought I was adequately sized but like they say 'size isn't everything.' I have a Worcester35CDi currently running off the end of my 22mm NG pipe. I was playing with the idea of replacing it with a Worcester38CDi but the British Gas salesman says it will not run off my 22mm pipe. Having formed the view that this should be an easy calculation and that someone somewhere must have produced a formula and that every CH engineer must be in possession of and using this formula everyday I am now wondering whether the formula in common use is the one where we suck our finger and hold it aloft to the wind.
 
Last edited by a moderator:
From the figures you have given with the boiler on maximum rate at 4.12m3/h. The pipe run of this length will only deliver approximatley 3m3/h. So it looks undersize in its current state.
 
The manufacturer specifies a degree of pressure not volume. Worcester state that the bolier needs NG delivered at a minimum of 16.5mb. The calculation must involve pressure arriving at the meter (MP) minus loss of pressure caused by friction in the pipe (L) The question is - how do you calculate the loss of preesure from the meter to the boiler?
 
Reg Man has just worked it out for you, in terms of gas rate. This shows that BG are right and the pipework would be undersized and would need to be upgraded for the 38CDi to be fitted.
 
Cardigan are you gas safe registered?

I am a retired mathematician and sometime DIY'er and although I would not attempt to tinker with anything involving my gas boiler I do like to understand what I am being told.
 
Thanks and thanks for the link to the copper pipework doc there should be enogh infor inthere for me to saiisfy my desire for a formula
 
You could post here, see if there is anyone local to quote against British Gas
[DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]
 
The manufacturer specifies a degree of pressure not volume. Worcester state that the bolier needs NG delivered at a minimum of 16.5mb. The calculation must involve pressure arriving at the meter (MP) minus loss of pressure caused by friction in the pipe (L) The question is - how do you calculate the loss of preesure from the meter to the boiler?

21mbar working pressure at the meter then should have 20mbar on the inlet to the boiler. BS6891
 
Hi

Can anyone tell me the flow rate in cubic meters per hour of natural gas from the meter in an oridinary residential domestic dwelling house

TIA
 
Hi

Can anyone tell me the flow rate in cubic meters per hour of natural gas from the meter in an oridinary residential domestic dwelling house

TIA
No, cos it depends on what appliances are connected. (there is a maximum that each type of meter will pass).
 
No, cos it depends on what appliances are connected. (there is a maximum that each type of meter will pass).

Thanks - can you tell me how I find out what the flow maximum flow rate I should expect to get from my meter?
 
i think he's asking for the caloric value,but i might be wrong
 
Status
Not open for further replies.

Similar plumbing topics

Thank you for the replies. I had another...
Replies
4
Views
904
More than fine then in 11/5 tube should be...
Replies
3
Views
679
LPG lock up pressure can be regarded as the...
Replies
4
Views
1K
Well if you are getting the gas meter moved to...
Replies
5
Views
3K
Back
Top