Scott_D Esteemed Plumber Gas Engineer Subscribed Messages 6,128 Oct 10, 2018 #1 I'm fitting a nest at my house to try it out. WB junior (don't ask) Does the nest heat link / hub need to be earthed? Can't find anything in the book
I'm fitting a nest at my house to try it out. WB junior (don't ask) Does the nest heat link / hub need to be earthed? Can't find anything in the book
ShaunCorbs Super Moderator Staff member S. Mod Plumber Gas Engineer Subscribed Messages 34,709 Solutions 1 Oct 10, 2018 #2 No it doesn't it's double insulated eg plastic
townfanjon Esteemed Plumber Gas Engineer Subscribed Messages 8,627 Oct 10, 2018 #3 scott_d said: WB junior (don't ask) Click to expand... Shakes his head and tuts !!!
Harvest Fields Esteemed Plumber Gas Engineer Subscribed Messages 10,441 Oct 10, 2018 #4 I have always wired the Earth in. But I have always had an Earth to wire in.
M MOSSEP Oct 12, 2018 #5 BS 7671 requires an earth at every point in wiring and at each accessory - reg 411.3.1.1 Even if it doesn't need it you should have an earth wire there and terminate it in the earth terminal.
BS 7671 requires an earth at every point in wiring and at each accessory - reg 411.3.1.1 Even if it doesn't need it you should have an earth wire there and terminate it in the earth terminal.