Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Nest with oil combi compatible? in the Boilers area at Plumbers Forums

Millsy 82

Plumbers Arms member
Plumber
Gas Engineer
Messages
4,350
I wired up a nest with an oil combi and whilst the heating side works fine is the hot water side compatible?

It seems to me that it doesnt work with an oil combi so I just turned it off.

Am i right or wrong.
 
It’s only on or off so should be
 
I wired it up as you would imagine common from boiler to nest number 5 then back to boiler on 6 but didnt work.

Did you try linking the nest out ?
 
Photo of nest to combi wiring mate.

63B9929D-C5F4-46FD-887D-D54D11442FF3.jpeg
 
Did you try linking the nest out ?

Yes in the end I left it with no programmer on the hotwater and left it on constantly as the customer said they were happy with that. Now they would like it so they can turn it off.

It's been a couple of months since I was there and I cant remember what the problem was but I wired to 5/6 set it to combi and it didnt work (obviously only set up for gas combi so not needed) so i then set it as a system boiler and for some reason wouldnt work again. I will go back and try it again.
 
Yes in the end I left it with no programmer on the hotwater and left it on constantly as the customer said they were happy with that. Now they would like it so they can turn it off.

It's been a couple of months since I was there and I cant remember what the problem was but I wired to 5/6 set it to combi and it didnt work (obviously only set up for gas combi so not needed) so i then set it as a system boiler and for some reason wouldnt work again. I will go back and try it again.

That’s why needs to be set for sys or heat only etc

That side is disabled when you choose Combi
 
Unfortunately doesn't give control other than on or off. Designed for gas combis.

Did a lot of hair pulling, well if i had any to start with, the first time I came across it on an oil combi.
 
Hello everybody.

Just spoken to nest regarding this problem that I had as I have just had the exact same problem on a system boiler.

What it is is the bacteria prevention is on causing the boiler to fire constantly for hot water.

To turn it off go

settings- equipment- bacteria prevention- disable.
 

Similar plumbing topics

D
Hi all, i moved recently in new home and...
Replies
0
Views
674
Dobsuk
D
    • Like
Great summary and well done for getting it...
Replies
1
Views
2K
At the moment when you move the hot water...
Replies
12
Views
1K
Yes everything worked fine before. Is there a...
Replies
6
Views
926
Back
Top