Hi folks,

I assume this has been asked many a times, so I do apologise in advance. My boiler which is only 6 months old started to lose pressure in March. My plumber applied 2 bottles of Fernox F4 express sealer and it seemed to fix it. It has again started to lose pressure, not drastically, maybe 0.20 bar in 24 hours. I have applied 2 more bottles to the F4 express, I'm sure however a plumber would have done a better job with it. I'm not a DIY person by any stretch of the imagination. I then turned the heating on for 1 hour at approx. 22 degrees celsius to allow it to circulate. I then let it cool down and stuck the heating on again for 1 hours at approx. 15 degrees. It is still dropping every day by about 0.05-0.10 bar a night. There is def. a leak somewhere as I had the boiler checked over by Ideal and they said there was no fault with the boiler. I have recently extended and have laid down marble flooring all downstairs and the new pipework is running under the floor and there is no chance that I want to rip any of it out. I read somewhere but i can't find the page now, that it was possible to install a device which constantly kept the pressure at say 1.5 bar without the need to repressurise every few days. Does anyone know of this and would you recommend? Alternatively, other than ripping out the floor, what other options do I have?

Thanks,

Kash
 
1. Losing 0.1 bar a day is too much. Having to adjust the pressure every 6 months is acceptable.
2. Whenever you replenish the pressure your are letting fresh water into the system. This water contains dissolved oxygen which will eventually cause steel components (radiators) to rust from the inside out. So even if the "constant pressure" device exists (e.g. a pressure reducing valve set to 1.5 bar) using it is just disguising the symptoms and will damage your system over time.
3. I would suggest:
3a. Re-pressurise the system to 1.5 bar.
3b. Isolate the boiler flow and return pipes at their valves under the boiler.
3c. Do not run the boiler for a period of 24 hours.
3d. If the pressure still drops then the fault is within the boiler.
3e. Open the valves, and wait a further 24 hours. If the pressure then drops, the fault is within the system.
4. If the fault is in the boiler, get a decent engineer to fix it.
5. If the fault is in the system, then considering your floors I'd suggest a leak detection specialist to determine where the leak is.
6. Note re. isolating the boiler (3b. above). The valves used are often poor quality and may leak when operated. They would then need to be replaced, and are often ridiculously expensive for what they are.
 
1. Losing 0.1 bar a day is too much. Having to adjust the pressure every 6 months is acceptable.
2. Whenever you replenish the pressure your are letting fresh water into the system. This water contains dissolved oxygen which will eventually cause steel components (radiators) to rust from the inside out. So even if the "constant pressure" device exists (e.g. a pressure reducing valve set to 1.5 bar) using it is just disguising the symptoms and will damage your system over time.
3. I would suggest:
3a. Re-pressurise the system to 1.5 bar.
3b. Isolate the boiler flow and return pipes at their valves under the boiler.
3c. Do not run the boiler for a period of 24 hours.
3d. If the pressure still drops then the fault is within the boiler.
3e. Open the valves, and wait a further 24 hours. If the pressure then drops, the fault is within the system.
4. If the fault is in the boiler, get a decent engineer to fix it.
5. If the fault is in the system, then considering your floors I'd suggest a leak detection specialist to determine where the leak is.
6. Note re. isolating the boiler (3b. above). The valves used are often poor quality and may leak when operated. They would then need to be replaced, and are often ridiculously expensive for what they are.
Thank you for your prompt reply.

I am how the kids say these days a "noob" with all this; how would I isolate the boiler flow and return pipes at their valves? If I know how to do this, I can do the said tests. I have attached a photo of my valves in their current positions.
 

Attachments

  • Boiler middle.jpg
    Boiler middle.jpg
    367.6 KB · Views: 33
  • Boiler left side.jpg
    Boiler left side.jpg
    323.8 KB · Views: 34
  • Boiler right side.jpg
    Boiler right side.jpg
    325.5 KB · Views: 32
You say the boiler is 6 months old and started losing pressure around March time, when did you have the extension built, around March, or later?
 
Did it loose pressure/ did you notice before the floor went down ?
 
Did they screw anything to the floor ?
 
Over a timber or concrete floor ?
 
If they’ve gone straight over floor boards them tiles are going to come up anyway
 
So they screwed something on top of the floorboards ?
 
That’s going to fail due to flex
 
Due to movement the floor / screed will crack
 
What Shaun is saying is that floorboards are not suitable for screeding onto these are typically fixed at 600 mm centres into a joisted floor, there is to much flex and movement in those boards to accept a screed , these boards need either fixing securely cleaning down priming and over laid with Hardi backer cement type board laid with a flexible tile adhesive and screwed at 300 mm centres before priming and fitting the floor tile , or removing and replacing with a no more ply type flooring before tiling onto . Kop
 
Last edited:

Similar plumbing topics

the op says no water in prv balloon so not prv...
Replies
7
Views
1K
You might have a EV (expansion vessel)...
Replies
7
Views
615
What the easiest way to find why my boiler is...
Replies
0
Views
548
Ok great...really hoping it wasn't a leak.
Replies
6
Views
703
Thanks for the reply, I’ll try your...
Replies
4
Views
892
Back
Top