Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss New radiator goes cold after an hour in the Plumbing Jobs | The Job-board area at Plumbers Forums

Messages
9
Hi guys please be nice I'm not in the trade ☺️

Fitted two rads yesterday to an existing system one to replace an old one and another one totally new and extended the rad circuit. The issue I have is they warm up perfectly but after about an hour or so one goes cold. The rad isn't the last in last in circuit the other new one comes after it. I've used this rad Kudox Premium Type 21 Double-Panel Plus Single Convector Radiator 600 x 1200mm White with this Drayton RT212 White / Chrome TRV & Lockshield 15mm x ½".
Does the trv have a built in thermostat which is cutting the feed as the room has hit temperature? There is no other room thermostat. I'm thinking this is the issue but was hoping someone could confirm this.

Cheers Andy
 
pic of the rad and pipework
 
Thanks guys and sorry.. So basically find the manifold and connect the new directly to that so the rads aren't sharing the feed and then the rads will get the heat benefit. One last question from what you can see it's not dangerous atm or what I have done could it damage the boiler? Really sorry to bother you guys I really wouldn't ask but if I could afford to get someone I wouldn't have done this.
 
theres your reason
 
Should be alright though if you balance the system?
You might also have an air lock in that leg. If it’s on s drop down. Feel the glow pipe running wall. If it’s only hot at the top, it’s an air lock.
Turn all other rads off to get it going, then balance the system.
 
Hi again guys funny thing is it cloudve been the trv or balancing. I've done some adjustment to both and the radiator is staying on all the time now and every radiator is running red hot. When looking at the balancing around the house every lockshield was fully open so I'm guessing these rads had no chance really. I really do appreciate the time and effort you his took in trying to help me out I really appreciate it
 

Similar plumbing topics

You seem to have got it sorted, but for future...
Replies
7
Views
944
  • Question
Will be a 15-60 then prob ups2 Green lights ?
Replies
8
Views
933
Yes I’d do that too, just shut the radiator...
Replies
5
Views
784
Thanks :) . A happy new year to you!
Replies
23
Views
1K
S
No point in doing anything with the radiators...
Replies
1
Views
865
Back
Top