Can anyone help with the following issue;
I had UFH system installed last year for my kitchen extension, the system was working ok when the plumber finished but as it was completed in the summer months the system was left off until required during the winter months but when I tried to run it I found the following:-
1/ zone valve opens to feed the pump OK.
2/ pump starts and water starts to flow through both of the UFH coils as indicated on the manifold flow indicators.
3/ Thermostatic valve is set to mid position 45.
4/ Temperature on the manifold inlet coils start to warm up and the return coils start to cool as the cold water from UFH returns to the outlet manifold.
5/ after 2 or 3 minutes the flow indicators start to drop back indicating no flow?
6/ increased the Thermostatic valve to Max and the flow indicators start to show a flow again but quickly drops off to show no flow?
7/ when I check the return coils to the outlet manifold they are still quite cold.
8/ when I check the thermostatic valve return to the boiler it is very hot.
My first thoughts were to check for air in the system and I did find quite a bit of air which I dealt with by refilling and flushing through each coil but the no flow problem still exists.
I think I will now have to remove the thermostatic valve and check for any blockages.
Any thoughts or advice on this issue would be very welcome.
Thanks in advance, Cliff.
see attached pics.
Can anyone help with the following issue;
I had UFH system installed last year for my kitchen extension, the system was working ok when the plumber finished but as it was completed in the summer months the system was left off until required during the winter months but when I tried to run it I found the following:-
1/ zone valve opens to feed the pump OK.
2/ pump starts and water starts to flow through both of the UFH coils as indicated on the manifold flow indicators.
3/ Thermostatic valve is set to mid position 45.
4/ Temperature on the manifold inlet coils start to warm up and the return coils start to cool as the cold water from UFH returns to the outlet manifold.
5/ after 2 or 3 minutes the flow indicators start to drop back indicating no flow?
6/ increased the Thermostatic valve to Max and the flow indicators start to show a flow again but quickly drops off to show no flow?
7/ when I check the return coils to the outlet manifold they are still quite cold.
8/ when I check the thermostatic valve return to the boiler it is very hot.
My first thoughts were to check for air in the system and I did find quite a bit of air which I dealt with by refilling and flushing through each coil but the no flow problem still exists.
I think I will now have to remove the thermostatic valve and check for any blockages.
Any thoughts or advice on this issue would be very welcome.
Thanks in advance, Cliff.