Hello all,
I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring, probably not been used until recently now it's colder.
When heating is called for, the boiler fires up ok but soon shuts down the heater as the temperature rises fast. The pump is going but no heated water is flowing around the external heating circuit. The diverter valve is pulled down.
It seems as if the heated water is being circulated around boiler like it should for DHW, the plate heat exchanger is getting hot. But without the flow to the radiator circuit it would overheat quickly.
I don't know if the reaon there's no heating flow is because the boiler has shut it down, or because there is no heating flow then the boiler has shut down.
So what am I missing? All forum enquiries about this sort of problem point towards pump & diverter, but here they 'seem' fine. Any suggestions on what to try next?
Some thoughts
1. Pump: it is spinning. I took out the AAV, small sign of weeping, it was pretty crusty, replaced with new one, that part now working fine but not solving my problem. Maybe pump its not providing enough pressure to push the water through the radiator circuit?
2. Diverter valve: the motor seems to actuating it upwards for DHW and downwards for heating correctly. I took out the rubber valve & paddle which was pretty crusty and marked, replaced with new one, but not solving my problem. Maybe its not actuating fully, so water hot water is finding a lower resistance path through the plate heat exchanger?
3. Blockage: maybe I have a blockage in the flow/return circuit or even in the plastic manifolds inside the boiler?
4. Bypass valve: not sure exactly how this operates but maybe if its stuck then that could explain why water isn't flowing around heating circuit when diverter valve suggets that it should be.
Some observations
a. The pump seems to run faster when providing DHW but slower after failing to provide hot water. Maybe this is a normal recirculation cool down speed?
Some History
A. The pump siezed last winter with kettling. It was tapped and normal operation resumed.
B. At end of last winter I decided to flush system, put in Fernox F3 to clean for a week, thoroughly flushed then Fernox F1 inhibitor. Had a slight pressure loss, couldn't find leak so added Fernox F4 leak sealer which didn't nothing, I eventually found leak and repaired.
I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring, probably not been used until recently now it's colder.
When heating is called for, the boiler fires up ok but soon shuts down the heater as the temperature rises fast. The pump is going but no heated water is flowing around the external heating circuit. The diverter valve is pulled down.
It seems as if the heated water is being circulated around boiler like it should for DHW, the plate heat exchanger is getting hot. But without the flow to the radiator circuit it would overheat quickly.
I don't know if the reaon there's no heating flow is because the boiler has shut it down, or because there is no heating flow then the boiler has shut down.
So what am I missing? All forum enquiries about this sort of problem point towards pump & diverter, but here they 'seem' fine. Any suggestions on what to try next?
Some thoughts
1. Pump: it is spinning. I took out the AAV, small sign of weeping, it was pretty crusty, replaced with new one, that part now working fine but not solving my problem. Maybe pump its not providing enough pressure to push the water through the radiator circuit?
2. Diverter valve: the motor seems to actuating it upwards for DHW and downwards for heating correctly. I took out the rubber valve & paddle which was pretty crusty and marked, replaced with new one, but not solving my problem. Maybe its not actuating fully, so water hot water is finding a lower resistance path through the plate heat exchanger?
3. Blockage: maybe I have a blockage in the flow/return circuit or even in the plastic manifolds inside the boiler?
4. Bypass valve: not sure exactly how this operates but maybe if its stuck then that could explain why water isn't flowing around heating circuit when diverter valve suggets that it should be.
Some observations
a. The pump seems to run faster when providing DHW but slower after failing to provide hot water. Maybe this is a normal recirculation cool down speed?
Some History
A. The pump siezed last winter with kettling. It was tapped and normal operation resumed.
B. At end of last winter I decided to flush system, put in Fernox F3 to clean for a week, thoroughly flushed then Fernox F1 inhibitor. Had a slight pressure loss, couldn't find leak so added Fernox F4 leak sealer which didn't nothing, I eventually found leak and repaired.