S

sox

just fitted a shower pump to the expance pip of cylinder but now there is no hot water to the rest of the house. the hot water runs for about 4mins & the pressure is low
 
Perhaps the pump is using off the water off the hot supply and pulling air down the expansion pipe?

Did you branch into the expansion pipe or fit a bos on to the top of the cylinder for the pump.

Have a look at the Essex flange site.
 
Is it only a problem with the pump running?

Check supply pipe from DHW tank - is the gate valve fully open? Is it all in min 22mm pipe?

Reconnect to cylinder with Essex flange
 
As Bernie has already pointed out, if your pump is on the vent pipe (expansion) it is in the wrong place . It will pull the column of water down the pipe and will then let air in which it sounds like is giving an air lock, rather than pulling hot from the cylinder . Pump needs alternative feed I would guess
 
thanks for all the tips on the hot water but the problem was a gate valve on the cistern was stuck closed. but now have anther problem can seem to get hot &cold water thrugh the pump to the shower. pump is not connected to the main supply
 
Try it with the pump connected before you alter anything.

Is the pump positioned correctly (i.e. level or near to level with the bottom of the cylinder)? Have you used 22mm pipework for your shower pump feed and supply runs for both hot and cold? (not critical for low volume pumps (eg 1.5 bar) but if you have higher pressure pumps (2.5 bar plus) it is important)
 
how can you tell if your pump is pull air from your expance pipe & if i turn off the gate valve at the tank to the cylinder & drain off the radiator at the lowist point would it then be possible to change a radiator
 
Are you saying you have a primatic or direct cylinder (as opposed to indirect)?

An indirect cylinder has a separate coil inside through which the primary circuit runs, keeping the heating water separate from the domestic hot water.
 
If its still a problem, then yes. However I would suggest an Essex flange as the apreture is larger. Put it as high up the side of the cylinder as you can before the domed top.

If you are wanting to change a radiator, look in your loft and see if you have 2 tanks. The smaller is for the heating circuit. See other threads about the subject - already covered in depth.
 
Last edited:
there are three tank in the loft two large & one small tank

tested the pump, cold run ok but the hot run for about 5mins then stops could this be because i have fittered the pump 1/2 way down the expance pipe & not fittered a surrey flange
 
Last edited by a moderator:
Sounds strange. Are the two large tanks connected together or do you have two separate systems?

if it were a problem with the expansion pipe I would have thought the problem would be from the start and not just afer 5 mins.

Have you checked you aren't running out of water in the tank in the loft when the hot stops?
 
I've also seen two tanks, with one connected to the other by a 22mm pipe in the bottom and the one without the water flowing into it full of slime and fungus.
 

Similar plumbing topics

C
  • Question
Thanks for replying matey. You've been a...
Replies
3
Views
1K
  • Question
hi have been a plumber for 50 years this month...
Replies
1
Views
834
  • Question
What type of cylinder do you have?
Replies
6
Views
1K
  • Question
IME Mira showers of that age are usually very...
Replies
1
Views
617
  • Question
Not to my knowledge but they're not things I...
Replies
4
Views
1K
Back
Top