I have a 20 year old Megaflo system driven by a oil boiler, and never had this issue before. The water in the tank is cold, the system is switched to on, but nothing happens - the boiler isn't heating the water. I know the boiler is functioning otherwise, as is the pump because I can turn the central heating system on and the boiler fires and the pump pumps.
I'm assuming there's an electrical problem then: tank thermostat being the first suspect. The Honeywell 2way valve to the tank is closed, and when I move it manually to the open position, again, nothing happens (would I expect the boiler to fire and the pump to operate?)
This may be a coincidence but a hot water tap in a mainly unused shower room had been left slightly open for several days. The electric immersion has been used for hot water topping up due to guests being here so we didn't notice the issue until the immersion was switched off.
Is there something else I may have missed?