guys I am just interested in what would be your plan of attack on this one .

Large house, the home owner inherited this problem so we dont know if its been like this from day one ...
I am incredibly busy and dont even want to do it ..

18 ish rads , 35 kw vokera bag of shi* system boiler . 3 rads furthest away form boiler dont heat up .

No stuck trv pins , open l/s , shutting other rads of doesnt seem to make any difference .

I put a new pump in a fortnight ago , no difference.

As said just interested in where you would start. Go for it lol

Thanks in advance .
 
Pump too small 25-80 pump needed

Also bet the expansion vessel is too small around 20 l needed
 
Pump too small 25-80 pump needed

Also bet the expansion vessel is too small around 20 l needed

Easy way to tell shut 5 rads do the others heat up ?
 
Vessel wont make any difference to rads not heating, pump is genuine Vokera , so I dont really want to put another one in , but have no idea what size it is to be fair .

True but find there regularly undersized
 
Personally, Id start with shutting all rads down but one of the dodgy ones (opened up fully). See then if anything happens and try bleeding to see what emerges. Id then try closing the bypass, if there is one, to try to get it to force its way - turn pump up full pelt and bleed again.

If that doesn't get something through there is def a prob :eek: and you're busy for the next 5 years. If it does something, do same with other two till the crap is distributed.

You will also prob find you'll disturb a load a junk if its not been flushed recently. That then, as you well know, means **** loads more work...

Come on Town. If you need something doing, ask a busy man!!:)

EDIT: Bu66er. Missed the other posts
 
Fit a cheap low loss header to the boiler and a suitably sized pump,to the rads. Probably getting lots of restriction through the boiler.
Give it a good flush while your on.

Boilers too old mate , not worth the work and expence , think its about 9 ish years . Like most customers hes after a quick fix for this winter , maybe a new one next summer
 
Not worth getting involved if he wants a quick fix it won't work
 
Cut a ups2 into the feed for the three rads and stick a 3 pin plug on it.

It really wanted to be sorted in the warm weather.

I'd be tempted to tell him to get three electric heaters and put some time in the diary when you are quieter.
 
I'd be tempted to tell him to get three electric heaters and put some time in the diary when you are quieter.

Lol, I am ready to do that when I see him , the 3 rooms are 2 bedrooms ( they dont use either of them ) other room is an office . Him , her and a 4 year old in a huge house . They want to walk round in bleeding T shirts and vests . The youth of today , gaud help us !!!
 