Hi all
I have just AR'd a Certikin MB 155 swimming pool boiler which was installed in a garage as I could see no ventilation openings direct to outside. The manufacturers instructions stated a minimum of 351cm2 high level ventilation and 702cm2 low level ventilation, I couldnt see any. There was no door louvres, the window had no vent or wasnt openable, there were no air bricks anywhere, and no penetrations through the pitched roof other than the flue.
Hiwever, it has been installed for 7 years, flue is pulling fine, apparently the last guy to come out and have a look at it said it didnt need any extra ventilation because of the height of the roof, there was plenty of air for the boiler. that didnt cut it for me, and I AR'd it. Opinions appreciated.
I have just AR'd a Certikin MB 155 swimming pool boiler which was installed in a garage as I could see no ventilation openings direct to outside. The manufacturers instructions stated a minimum of 351cm2 high level ventilation and 702cm2 low level ventilation, I couldnt see any. There was no door louvres, the window had no vent or wasnt openable, there were no air bricks anywhere, and no penetrations through the pitched roof other than the flue.
Hiwever, it has been installed for 7 years, flue is pulling fine, apparently the last guy to come out and have a look at it said it didnt need any extra ventilation because of the height of the roof, there was plenty of air for the boiler. that didnt cut it for me, and I AR'd it. Opinions appreciated.