Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Noisy Worcester in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

Sid Viscous

Plumbers Arms member
Plumber
Gas Engineer
Subscribed
Messages
261
Hi guys, been to look at an old 35CDi II. Works fine on c/h, but open a hot tap.... boiler fires, heats up, starts knocking, pressure gage jumps about a bit, then it goes out. 10 secs later starts all over again. The pin in the diverter moves across ok & stays in dhw position while ever a hot tap is open, moves back fine when closed. It does this whether or not the heating's on. Don't know if this is normal for this model but when c/h is on & you open a hot tap, both c/h and dhw lights are on. Most other boilers I've come across switch between the 2.
Any idea please
 
I'd be looking at the phex sounds like it's totally clogged up.
 
I would be looking at sticky div valve first then looking at plate chocked up. Should have about 10-15 deg difference across the plate.
 
Hmm, don't like the sound of any of those! I'll check 'em out though. I'm gonna have to get myself on a course soon!
 
You could have an issue with that diverter valve, if the ch is off does it start to pass down the heating when you run the tap? I've had this before on Duo Tecs and it's been the diverter and the plate. All the signs of a dirty system. Basically the boiler tries to heat up the dhw, but cause of the diverter slightly letting water through and the plate being blocked, it can't so starts to kettle.
 
you can pull the diverter actuator motor off and operate the diverter by hand to eliminate that. then check the plate. as above you could check for temp diff across the plate but never had much joy doing that
 
As I said in OP, you can see the pin on these from underneath & that's moving full back & forth & staying rock steady all the while. So is arran saying look for a bit of heat down the flow pipe with c/h off?
 
Put it in hot water only and if the flow/rtn get any heat down them the divertor is passing. Is the dhw thermistor ok? What about flow switch?
 
from what I was told on the course if it is passing due to worn diverter seat the diverter arm can be turned 180 degrees as temp measure
 
That's right, but from experience the diverter valves rarely pass on modern Greenstars so I would be pointing more towards the plate.
 
strangely enough, I did a service on that same model yesterday. Custard complained that it doesn't heat up as fast as her previous house? She bought the property and moved in on Monday.
I told her it might be due to sludge or a scaled HE. She then wanted to know how old the boiler was? I said about 12-15 years? Really, she says?

So in her presence. I phoned Worcester Bosch. The staff on the line just kept telling me that they have all the parts, so there should be no problem. Custard wasn't interested. She WANTS ME TO BOOK HER IN FOR A NEW BOILER WHENEVER I HAVE SOME SLACK TIME?

Now, we need more proactive customers like this.
 
you can pull the diverter actuator motor off and operate the diverter by hand to eliminate that. then check the plate. as above you could check for temp diff across the plate but never had much joy doing that
Is this not the old 35cdi II rsf we are referring to? Not the newer greenstar model!
 
Status
Not open for further replies.

Similar plumbing topics

Chris, just to update, thanks for all your...
Replies
3
Views
678
Do you find a solution, I have exactly the...
Replies
11
Views
2K
tinodj
T
I replaced the actuator last night and all is...
Replies
9
Views
2K
Just for completion, and to have this archived...
Replies
8
Views
2K
Yeah the system was quite dirty when drained...
Replies
2
Views
1K