Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Oil Boiler - High Carbon Monoxide Readings in the Boilers area at Plumbers Forums

Status
Not open for further replies.

WHPES

Plumbers Arms member
Plumber
Gas Engineer
Messages
4,830
I'm getting high CO readings from a customer's oil boiler, typically 250ppm

Obviously problems with aiflow, worn nozzle, poor baffle cover seal, and flue problems are what one would expect, however are there any other possible causes I am missing?

And yes....I did tell the customer not to use it and I disabled it before leaving.
 
Last edited:
Oil pressure? And check the filter too.
 
Last edited by a moderator:
I messed up my FGA a week or two ago and it was reading 635ppm CO .... outside!! Luckily a couple of days later it sorted itself out.

This started because I was having high CO readings after a service - smoke was sort of okay and in went the FGA. After an hour the F wasn't standing for flue ... but French:confused:

It took me another hour or so to establish the new nozzle was faulty. So next time my CO2 is sort of okay but CO is high, I'm changing the nozzle.
 
Stuffed a rag in the flue, put a couple of smoke pellets in the chamber and set the fan running. The internal part of the balanced flue spewed smoke out along its entirety like a sieve.
 
Status
Not open for further replies.

Similar plumbing topics

Update: I couldn't get hold of a heating...
Replies
5
Views
2K
Less than 350ppm is acceptable according to...
Replies
2
Views
2K
Think the appropriate phrase for this should...
Replies
4
Views
1K
I know it's very hard to know for sure but...
Replies
5
Views
10K
Back
Top