Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Oil central heating flue in the Boilers area at Plumbers Forums

Status
Not open for further replies.

SMB

Messages
52
Hi,
Searched but unable to find the answer.
The flue appears to have a central pipe (exhaust gases) with an air intake around it, just like our own gas boiler flue. However it is positioned below an opening window, but slightly to one side.
What are the regulations concerning flue placement near to an opening window.
So how close can it legally be in both directions.
Thanks
 
What boiler is it?

Sorry, don't know.
The boiler is an oil fired combi boiler, ie no hot water storage tank in the house.
It is in the house that my daughter has moved into and I have slight concerns.
 
Sorry, don't know.
The boiler is an oil fired combi boiler, ie no hot water storage tank in the house.
It is in the house that my daughter has moved into and I have slight concerns.

how close is it to the window opening ?
 
Looked at a few different mi's by different manufacturers.

The clearances for both SE and HE models are the same.

Take a butchers at this.

Screenshot_2016-10-28-21-04-46.jpg
 
The distance is greater than those in the table.
MANY thanks Croppie, never thought of going through mi instructions.
You have put my mind totally at rest.
Cheers
SMB
 
Status
Not open for further replies.

Similar plumbing topics

Np Simon. Hoping to get the boiler engineer...
Replies
4
Views
880
As a precaution report this to the building...
Replies
1
Views
1K
Yeah I think there was loose wiring in the...
Replies
6
Views
851
Hi Guys Im doing a new build near Brecon...
Replies
0
Views
1K
In principle it's should not drip but in...
Replies
2
Views
6K
Back
Top