Hi all
I have a warm flow boiler with a Riello RDB1 90-120 burner
It started to randomly lockout some time ago and an engineer changed the photocell and solenoid without success
I was told by the local plumbing wholesalers they had been supplying a lot of pumps recently for Riello burners as something about the oil being supplied in our area ( north highlands ) was making them fail prematurely.
I changed the pump with no result still randomly locking out sometimes after a few minutes or an hour or so.
I was advised to add an oil conditioner treatment so got some and added it to the tank and within a short time the lockout problem disappeared.
Anyone know what this is? Could it be just the oil or possibly a nozzle or fire valve problem ?
I have had another fill since and tried it without conditioner in the oil and the lockout problem came back then went away as soon as I added conditioner.
I have a warm flow boiler with a Riello RDB1 90-120 burner
It started to randomly lockout some time ago and an engineer changed the photocell and solenoid without success
I was told by the local plumbing wholesalers they had been supplying a lot of pumps recently for Riello burners as something about the oil being supplied in our area ( north highlands ) was making them fail prematurely.
I changed the pump with no result still randomly locking out sometimes after a few minutes or an hour or so.
I was advised to add an oil conditioner treatment so got some and added it to the tank and within a short time the lockout problem disappeared.
Anyone know what this is? Could it be just the oil or possibly a nozzle or fire valve problem ?
I have had another fill since and tried it without conditioner in the oil and the lockout problem came back then went away as soon as I added conditioner.