Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

  • Thread starter smitty
  • Start date
  • Replies 2
  • Views 833

Discuss oil rate in the Boilers area at Plumbers Forums

Status
Not open for further replies.
S

smitty

Don't know if this a stupid question but is it possible to oil rate an appliance in the same way that you gas rate an appliance
 
You can get oil flow meters so I suppose you could, but generally we rely on fitting the correct sized nozzle at the correct fuel pressure (this will only flow a certain amount of fuel by design very fine tolerances on nozzles)
 
No worries all the burners I'm working on at moment have flow meters curiosity always in my head of working out different methods
 
Status
Not open for further replies.

Similar plumbing topics

Any gas boiler's HEX can stand a static head...
Replies
16
Views
1K
External hounsfield heat only. If you really...
Replies
4
Views
998
  • Question
Sounds to me that the 15mm pipe that you are...
Replies
14
Views
1K
Essaboy
E
I have 2 oil pump pressure gauges, a Nu-Way...
Replies
0
Views
201
All fixed. Changing the nozzle and cleaning...
Replies
4
Views
548
Back
Top