Hi all,

Does anyone here have, by any chance, a list of outputs for the older myson roundtop radiators. The ones without the convector fins? A Landlord i do work for has been told by a damp "specialist" that the heating is undersized which is why there's black mold on the walls and windows! He's asked me to check out the system. Visually it looks undersized and the rooms aren't exactly the warmest, however I would like to give him an acurate assesment. Most of the radiators are the old Myson round-top type.

Bye the way, I don't think the mold has anything to do with the heating system, it's been in 30ish years and the only time the mold has been an issue has been since the new tenants moved in less than a year ago. Young family with a new born baby! They insist that they don't dry their clothes on the rads!

The house itself has no ventilation in any of the rooms, and is Double glazed! The mold is in the bedrooms upstairs! Just some additional info I thought you'd like to know. However if anyone has, or can direct me towards a chart of output sizes for the old round-tops I'd be mighty grateful.. :)

Cheers .. )

Steve
 
Ventillation cures Mold, not heating.

However if the rooms are already too cold and slow to warm up, then the Tennants may be reluctant to open the windows for a short period daily.

Seem to remember when fins came into being they upped the output by 50%
So to get back to non finned you need 66% of a finned rad of equal size (approx)
 
PREMIER HE radiator by MYSON


With vents in the back you can't get to, to change if the corners get rounded


Alas not the one's I'm after happyflyer ... I checked out Myson's website and did a search before coming here... :) Thanks for trying to help though :) the radiators I'm after do not have the convector fins and are around about 20-30yrs old!
 
Ventillation cures Mold, not heating.

However if the rooms are already too cold and slow to warm up, then the Tennants may be reluctant to open the windows for a short period daily.

Seem to remember when fins came into being they upped the output by 50%
So to get back to non finned you need 66% of a finned rad of equal size (approx)

Exactly what I told the Landlord snowhead :)

I don't know why the "expert" didn't notice the lack of ventilation .... Apparently he touched the radiators in the rooms, reckoned they were not putting enough heat into the room and that was the cause! Weird...!
 
Count it out at 1000 watts/m2 for singles and 1725 watts/m2 for doubles for a 50Δ T.
Not far away at that Steve.
 
I've always used this for old rads

[DLMURL]http://www.pipecasings.co.uk/downloads/download%20files/Radiator%20Output%20Calculator.pdf[/DLMURL]

Brilliant link Roger .. Many thanks.. Now down to some sizing work.
 
Last edited by a moderator:
I have found a couple of the old Thorn/Myson rad lists. Sadly I threw most out years ago & often wished I hadn't.
It should be noted that the outputs on old lists were rated too high.
Here are some rad sizes to give you something to work on & compare with.
Only double rad I can clearly remember the list output was a 21x45 double (no fins) which was I believe 4700 btus.
My old list has Myson HE round tops singles (non finned) 21" high rads - 37" long = 2315, 45" long= 2799, 53" long= 3280, 61" long = 3750, 69" long= 4238 btus.
I also have the 15" high & 27" high single rads outputs. Obviously for double sizes the output is a tad lower than double these singles.
 
Last edited:
Diamond,


Send me your email address I have found all the Myson data sheet for the old rads


Tony Hughes
 
myson.jpg

For those of you who only want the quick way of calculation, hope this helps, this is page
6 of 6

Tony

myson.jpg
 
Diamond no need for email this is radiator no fins, good luck, if
you want the outputs with fins i.e. convector type just say and I will post it

no fins.jpg
 
Last edited by a moderator:
Undersized, round top radiators. Sounds like one of the old seventies coal fire back boiler jobs.
 
Thanks to the info given here I can let the landlord know that the radiators are adequate :) Cheers once again :)
 
Status
Not open for further replies.

Similar plumbing topics

Central heating radiators - DIYWiki -...
Replies
1
Views
1K
Would others say this formula is accurate? If...
Replies
4
Views
6K
An old system may not even be designed to give...
Replies
18
Views
13K
I decided not to change the radiators and have...
Replies
6
Views
3K
Maybe the boiler has been set up to...
Replies
7
Views
1K
Back
Top